#10771 06/18/02 10:34 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
I'm installing a 60a sub panel on a residential home feeding it with a 60a breaker using #6 thhn, I should be able to use a 100a panel box for it and stay within the code, right?


The Golden Rule - "The man with the gold makes the rule"
#10772 06/18/02 08:48 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
yup.