Contractor used a EMT/IMC/RIGID connector on a service mast riser an I rejected it. He reported a complaint on me and said I was picking on him. I see a violation of the listing being used in a wet location. I also do not beleive this set up has adequate strength as requires in article 230. The service drop is 109' coming from across the road. He has called all the brass to go look at it with him. IMO this is NOT a code compliant installation.
- necbuff
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Wouldn't fly around here! Connector, or that strap? Looks like a drop holder without the insulator, used as a strap? Is the lower conduit EMT?
So this guy doen't own a threader, or too cheap to buy a listed theadless connector suitable for the purpose.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: May 2004
Posts: 697
Member
|
I think you nailed this one necbuff. I'm not an inspector, but it looks like he found an EMT fitting that would fit IMC, like maybe a 3"EMT connector would fit 2 1/2" IMC. He did it out of cheapness or ignorance, but it's wrong. He's looking at his cost to pull it apart & put it back together & look like a fool in the process. If he pursists, large EMT connectors sometimes are stamped with the size, which will show the error(the hub on the meter socket may be stamped with the IMC size). This could be a big leaker by capilary action.
Dave
|
|
|
|
Joined: Oct 2000
Posts: 2,725 Likes: 1
Broom Pusher and Member
|
This one seems like an easy one... but let's try it from "Another Angle" - Do any Set Screw Fittings exist, which are UL Listed as Weatherproof - namely EMT Set Screw Fittings?,
- Was there not a "little" issue a few Months back, with all Manufacturers of Compression Fittings for EMT losing UL Listings as to the Weatherproof abilities... and only one brand finally received Listing - and this was for Fittings DESIGNED for just that purpose?
Just seems very counter-productive (and stupid) to install a Set Screw EMT Fitting outdoors and in the path O' the Weather. Unless the Fitting is Listed for that purpose (if so, please let me know!!!), the Installation is "Caa-Caa Del Toro" (Bull Poo-Poo) Scott35
Scott " 35 " Thompson Just Say NO To Green Eggs And Ham!
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Yes you can get Die Cast Set Screw RMC/IMC connectors. Here is one company that makes them. Why you would want to use one is another story. In the larger sizes some set screw connectors are listed for RMC, IMC and EMT I have not seen or heard of any that are weather proof. That aside the service in the picture has a couple of violations that jump right out at ya. 230.28 and 344.42 This was brought up at another forum but I thought it was interesting. Are threaded conduit couplings listed as raintight? Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
That's right, compression connectors are only listed for rain-tight as you throw them over the border into Canada. (except that one company no-one around here carries) So necbuff, what is being used to support that riser? The hole that he cut in the roof? Those straps, I have not seen before, are those common anywhere else?
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Jul 2002
Posts: 680
Member
|
Are threaded conduit couplings listed as raintight?
Not sure one way or the other but running threads won't keep water so I don't see how they could be. They sure the heck are alot stronger than a set screw connector.
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Treaded couplings should be, after all with a small amount of pipe compound you could have it be gas tight! And, for older buildings Rigid Galvanized was common water pipe for a long time.
I usually add a little Noalox to the threads anyway, for ease of installation, wrench tight a little further that way. But we are looking for "Rain-Tight", not "Water-Proof".
Reguardless, a set screw is neither.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
The problem is that RMC threaded couplings as Walrus pointed out have running threads (not tapered) While the galvanized ones for plumbing have tapered threads. I do use RMC threaded conduits outside but I do not believe they are listed as raintight.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
Posts: 99
Joined: August 2003
|
|
|
|