Cable Company Grounding Methods #106433 04/09/05 06:01 AM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline OP
Moderator
Capt Al's neighbor had the cable company do some work. The neighbor asked Al to look at it and see if it was OK.

[Linked Image]

What do you all think of this?

Code Compliant?

Professional?

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
2017 / 2014 NEC & Related Books and Study Guides
Re: Cable Company Grounding Methods #106434 04/09/05 06:07 AM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline OP
Moderator
[Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Cable Company Grounding Methods #106435 04/09/05 07:50 AM
Joined: Dec 2000
Posts: 4,281
electure Offline
Member
From the '99 NEC (The current here in CA)
820-40 (b) Electrode. The grounding conductor shall be connected as follows.
1. To the nearest accessible location on the following:
a. The building or structure grounding electrode system as covered in Section 250-50
b. The grounded interior metal water piping system as covered in Section 250-104(a)
c. The power service accessible means external to enclosures as covered in Section 250-92(b)
d. The metallic power service raceway
e. The service equipment enclosure
f. The grounding electrode conductor or the grounding electrode conductor metal enclosure, or
g. To the grounding conductor or to the grounding electrode of a building or structure disconnecting means that is grounded to an electrode as covered in Section 250-32; or....

Sounds good so far, but 250-70 doesn't like that clamp.
3. For indoor telecommunications purposes only, a listed sheet metal strap-type ground clamp having a rigid metal base that seats on the electrode and having a strap of such material and dimensions that it is not likely to stretch during or after installation.

The Cu connection to the Al hub also is, I believe, a bust of 110-14, dissimilar metals

Code Compliant? I think not




[This message has been edited by electure (edited 04-09-2005).]

Re: Cable Company Grounding Methods #106436 04/09/05 08:15 AM
Joined: Jun 2004
Posts: 206
C
capt al Offline
Member
The 1/2" PVC in the first picture is protecting the GEC, which is connected to a ground rod. The cable guy did not run his ground wire to the nearest accessible location. I will be fixing this for my neighbor.

Al

Re: Cable Company Grounding Methods #106437 04/09/05 09:40 AM
Joined: Jul 2002
Posts: 680
W
walrus Offline
Member
as a public utility are they subject to NEC?

Re: Cable Company Grounding Methods #106438 04/09/05 09:56 AM
Joined: Oct 2000
Posts: 3,930
Bill Addiss Offline
Member
In a situation like this I once ran a small tail of #6 BC out of the bottom of the meter enclosure because I thought I had to make something available. The Poco inspector wanted it removed and accused me of drilling a hole for it too. [Linked Image]

Bill


Bill
Re: Cable Company Grounding Methods #106439 04/09/05 10:08 AM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline OP
Moderator
Bill that is too bad, I wonder what hazard the inspector saw in a grounded conductor? [Linked Image]

This why some say no good deed goes unpunished.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Cable Company Grounding Methods #106440 04/09/05 11:48 AM
Joined: Oct 2000
Posts: 3,930
Bill Addiss Offline
Member
Quote
This why some say no good deed goes unpunished.
Bob,

What made it worse was this was on a service upgrade and the Poco guy told the customer (I wasn't there) this was against code and I shouldn't have drilled a hole in the enclosure either, so you can imagine I got a call about it.

I explained to the customer the reason for the tail but told them I would come and remove it. (I asked if it seemed like the guy was drinking - I guess he's never seen the little KOs in the bottom of the enclosures).

Does anyone leave a tail like this?
I thought it (or something) was required per 250.94 in situations like the one pictured.

Bill


Bill
Re: Cable Company Grounding Methods #106441 04/09/05 03:18 PM
Joined: Jun 2004
Posts: 206
C
capt al Offline
Member
Bill what really makes the use of this clamp foolish, is the #6 GEC was exposed 12" below the cable splitter where it attached to a ground rod. The cable guy had to run more #10 to go to the meter hub and install his clamp.

The tail you ask about. I have never seen one at the meter, but have seen tails at the panel board for the cable & alarm guys to use.

Re: Cable Company Grounding Methods #106442 04/11/05 11:11 AM
Joined: Jun 2002
Posts: 58
E
energy7 Offline
Member
Ah! The "Cable Guys!!"
I check grounding of the cable installer whenever I get the chance. It's doubly important with powered cable (<=150 v to grd) (From all those new meter pedestals on each street corner).
Sometimes I get the comment from the cable installers that their work is not my business; they don't need a permit. After I give the recalcitrant ones a WRITTEN correction notice (with a copy to the job super) I explain that they still need to comply with Code req. even without a permit, I WILL comment on unsafe installs (80.23, 110.3 #8), and that, if not remedied, they could be disconnected and/or their system powered down(80.13).
In their defense, most installers, when shown the importance of proper grounding, end up revising their work to passable levels.

Page 1 of 3 1 2 3

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,263
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
BigB 5
Trumpy 1
dsk 1
Popular Topics(Views)
260,590 Are you busy
195,439 Re: Forum
184,766 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3