1 members (Scott35),
466
guests, and
10
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Oct 2000
Posts: 3,682 Likes: 3
OP
Administrator Member
|
This pic goes into the category of things you just know are wrong....but where is code violated? What you see is a duplex receptacle mounted in a 3-0 box. It is attached where the box cover usually attaches. There are covers made for this box that hold a single receptacle, but not a duplex. An oversize receptacle coverplate will just about cover the front of the box.
- renosteinke
|
|
|
|
Joined: Feb 2005
Posts: 219
Member
|
I just took a duplex just like that out of service today and it had a Raco Dup cover made of stamped steel.
Rob
|
|
|
|
Joined: Oct 2000
Posts: 2,723 Likes: 1
Broom Pusher and Member
|
I may have 1 or 2 scenarios to ponder as violations: <OL TYPE=1> [*] Is this Outlet Grounded (Box and Receptacle) - via an EGC? [*] Is there adequate free Conductor length in this Box? </OL> And the most obvious: Why no cover? (hee hee ...) Scott35
Scott " 35 " Thompson Just Say NO To Green Eggs And Ham!
|
|
|
|
Joined: Feb 2003
Posts: 939
Member
|
John :
i did see cover for 3-0 and 4-0 verison have duplex verison but i dont like it not much becasue the older cover only have single screw to hold the repectaile in place the later cover have two screw or three screw to really lock the repetcale in place i know Raco do make it
Merci , Marc
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
You learn something new every day....
I've never seen the duplex cover for the smaller (3-0) box...didn't know there was one. Maybe this is OK after all?
Sierra- sharp eye! You are correct, the old romex has no ground wire. As for "free conductor" length, that I'm not so sure about; back then there was no such requirement. Conductors often had insulation skinned off them as they passed through the box, and a very short pigtail twisted and soldered in place, then wrapped with tape.
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
Box should be a device box so that the device can be properly installed.
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
Joe, The manufacturers make covers for duplex recptacles in octgon boxes, so why would this be an improper installation? (assuming that the cover was actually installed) Don
Don(resqcapt19)
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
Don:
I am aware of that cover, and I am commenting on this "incorrect" installation.
The receptacle on the round cover is secured to the octagon box using the two 8/32 screws that are used to secure the entire assembly.
The installation here is not correct under any circumstances!
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
I've seen many of these that have the mounting ears/yoke cut off right at the recptacle. The receptacle is held to the cover with the single 6-32 in the center of the cover, while the cover itself is screwed to the box with the usual 8-32s.
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
Here is that cover --- and the proper receptacle is made without a yoke (strap) and the single 6/32 screw is actually a violation since this would be a "cover mounted" receptacle.
Joe Tedesco, NEC Consultant
|
|
|
Posts: 43
Joined: September 2013
|
|
|
|