#105316 09/06/04 07:43 AM
Joined: Oct 2000
Posts: 2,749
Member
[Linked Image from nachi.org]


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Joined: Mar 2004
Posts: 76
M
Member
Where do You start ?? Must not own any side cutters !
Around here, I would install a Disc, & run flex to the Waterheater. Makes a nice looking installation.
Is the romex #10 ??

Joined: Nov 2003
Posts: 269
E
Member
How could anyone walk away from this? [Linked Image]


John
Joined: Jun 2004
Posts: 206
C
Member
Always nice to leave the covers off of the elements. No one would ever put their hand near there.

Joined: Jan 2003
Posts: 4,391
I
Moderator
Do we know this is complete?

The breaker can be the disconnect.

It is tough to give answers without knowing the details.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Oct 2000
Posts: 2,749
Member
Bob:

This work was what the AHJ found during the Final.

Your opinion of what you see wrong here will be appreciated.


Joe Tedesco, NEC Consultant
Joined: Jan 2003
Posts: 4,391
I
Moderator
Well if this is what it looked for the final the inspector should fail it.

The only reason I can say for sure would be lack of support of the NM 334.30 and the open cover that Capt. Al mentioned 110.27(A).

The other issues, correct wire temp rating and lack of disconnect can not be commented on from this picture alone.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Oct 2000
Posts: 2,749
Member
Bob: Discussion!

That's healthy, and that is what we do here!

I make comments all of the time to help people understand the subject of the installation.

Pictures are always helpful, but cannot show every single item.


Joe Tedesco, NEC Consultant
Joined: Jun 2003
Posts: 1,143
D
Member
Without knowing the conductr size, here's a quick take...

Failure to secure NM cable within appropriate distance... (336-18 '96 NEC)

Failure to secure/support NM cable @ required intervals along run...(336-18 '96 NEC)

Failure to protect NM cable from physical damage... (336-6(b) '96 NEC)

Unprotected access to equipment (failure to install in an approved manner)... (422-6 '96 NEC)

Joined: Jan 2003
Posts: 4,391
I
Moderator
Doug you are Chicago sparky right? As such you may not be used to seeing NM but it is often run exposed.

In my opinion if it was supported properly without the loop to the floor, physical damage would not be an issue at least here in MA and RI. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Page 1 of 3 1 2 3

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Top Posters(30 Days)
Admin 14
Trumpy 10
Popular Topics(Views)
280,396 Are you busy
213,468 Re: Forum
200,382 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5