Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Oct 2003
Posts: 289
Member
|
how did they manage to overheat _all_ neutrals?
|
|
|
|
Joined: Mar 2004
Posts: 76
Member
|
How about a grounding bushing on that RGS entering the panel ??
|
|
|
|
Joined: Jan 2004
Posts: 615
Member
|
Is this the result of harmonic currents?
What is this panel feeding?
|
|
|
|
Joined: Nov 2001
Posts: 745
Member
|
Looking closely at the several neutral busses here, it appears that the burn/overheat marks are on the conductors which are attached to the top-most buss (the one closest to the breakers). I wonder if a poor connection exists where the two phillips screws connect this buss to the rest of the neutral assembly, causing this entire buss to heat up? Mike (mamills)
|
|
|
|
Joined: Jun 2003
Posts: 681
Member
|
Something here is definitely wrong. Not only the neutral connections to the bus, but even along the length of some of the conductors, it is discolored. HMMMM!! I am curious what is causing this.
Pierre
Pierre Belarge
|
|
|
|
Joined: Oct 2003
Posts: 147
Member
|
It looks like there are several ground wires terminated on the neutral buss, including the ground wire from the UF cable that was in the same conduit as the feeders.
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
I also was thinking triplen harmonics, but I assume this is a dwelling, and circuit 3 is a GFCI. What non-linear load(s) would you have on a GFCI circuit?
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Apr 2004
Posts: 812
Member
|
The overheated neutral bus bar and discolored wires aren't the only problems...
Where the heck's the main breaker?
Is there anyone on board who knows how to fly a plane?
|
|
|
|
Joined: Feb 2004
Posts: 1,438
Member
|
Theelectrikid: First off, Welcome to ECN! Chances are, the main overcurrent protection (breaker) is at the source for this panel.. In the eastern side of the USA, it seems to be popular, if not universal to have the power co.'s meter outside with a main disconnect.. This in-turn feeds to a distribution panel elsewhere.. (usually a garage or basement, which is what you see here... Protection from overloads for this type of panel would be at the source it was powered from.. (Main disconnect, branch circuit feed from another panel, etc.) -Randy
|
|
|