Honestly Now!!

Maybe those old ceramic wire-nuts were useful for something!

This is really scary!!

[Linked Image from hvacloads.com]


Joe Tedesco, NEC Consultant
Horizontal Ad
Joined: Aug 2002
Posts: 1,081
T
Member
That looks like it was a crimp-on lug connector...? Well, on 2nd look, maybe not, with the "spring" there. The other connectors are a similar yellow color.

Yes, that is scary looking. Reminds me of the crayons on the radiators in school [Linked Image]

[This message has been edited by ThinkGood (edited 12-31-2003).]

Joined: Aug 2002
Posts: 1,691
S
Member
The black stranded conductor has some of the "threads" nicked.

Ya think that could have contributed to the Marrette cheese? [Linked Image]

Joined: Oct 2003
Posts: 152
M
Member
Hey Joe, Do you have a more zoomed-out version of that picture? I would like to see what the rest of the conductors look like. There are hints that they are not in much better shape. [Linked Image]

Below is a picture of a situation I encountered in my first house. Remodeling contractor, that also thought he was an electrician, just didn't get that fourth wire far enough into the wirenut before he applied the twist. I keep this on my desk at work as a constant reminder of how important correct electrical splices are. [Linked Image]

[Linked Image from ww2.imagewiz.net]

[This message has been edited by Mean Gene (edited 12-31-2003).]

Joined: Oct 2000
Posts: 2,749
Member
Mean Gene:

No I found this on the HVAC site and this was the only one, but have asked the webmaster to put me in touch with the person who posted this picture there. There are many electrical hazards and that's one of the items we discuss here.

Your burned up termination at the splice is also scary.


Joe Tedesco, NEC Consultant
Joined: Oct 2003
Posts: 289
:
Member
coming to my point of view again, you wouldn't have ran into this with a wago (or a push-clamping one for stranded)........

Joined: Apr 2002
Posts: 2,527
B
Moderator
The “drooling” connector looks like it may be hopelessly undersized for the task, based on exposed strands of black conductor.

The assembly looks like a resistance/strip/duct heater, based on the definitie-purpose {vending-machine-grade} contactor, ceramic bushing and ‘therm-o-disk’ in picture. Looks like there is other evidence of localized overheating, possibly due to an intermittent/failed ‘indoor’ fan.

The black wire looks like part of some modification—maybe THHN “building wire” jury-rigged to red “appliance wiring material”—by an unqualified person.

What is the black crusty stuff [7 o’clock in picture] around red vinyl conductor? Gross overheating is likely, and needs detailed inspection/troubleshooting.

Horizontal Ad
Joined: Oct 2001
Posts: 135
W
Member
Joe
I sent you an email with info about the post.

I'm sure he will be glad to hear from you.

Joined: Nov 2002
Posts: 794
Likes: 3
W
Member
Quote
What is the black crusty stuff [7 o’clock in picture] around red vinyl conductor? Gross overheating is likely, and needs detailed inspection/troubleshooting.

I think it might be "friction tape" used for electrical tape. Which would mean that some unqualified handyman has been in there...

Joined: Aug 2003
Posts: 99
Member
IMO it looks like the black wire was not under the under sized wire nut, and was not properly pre-twisted to get the max surface area cunductor to conductor mating

Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
338,285 Are you busy
263,701 Re: Forum
244,031 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5