The shiny stuff is the slick outer covering of the wires burning --- v e r y s l o w l y ! ! in a M a r r i o t H o t e l in M e x i c o C i t y!!
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Oct 2003
Posts: 289
Member
|
what happened? overload or loose connection?
|
|
|
|
Joined: Oct 2003
Posts: 152
Member
|
My guess is improper torque at installation.
|
|
|
|
Joined: Oct 2003
Posts: 147
Member
|
"The end of the road, there aint more threads"? Was the wire too small for the connector, did the "electrician" tighten the connector untill it stopped, leaving the wire somewhat looses in the connector?
|
|
|
|
Joined: Aug 2002
Posts: 1,081
Member
|
They squeezed the wires so tight that it caused an electrical bottleneck.
|
|
|
|
Joined: Jun 2003
Posts: 681
Member
|
How come all three lugs are not the same color? Shouldn't they all be black? Mine are always black... after awhile . He probably did not cut off enough strands on C phase. Pierre
Pierre Belarge
|
|
|
|
Joined: Oct 2000
Posts: 2,749
OP
Member
|
PC .... That's it, I wasn't sure about that phase! Thanks for solving the puzzle! I always thought they were "polishing" the lug to sort of keep them clean.