ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (CoolWill), 250 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Oct 2000
Posts: 2,749
Member
[Linked Image]

OR was it because the rigid metal conduit was threaded into the T Conduit Body made of aluminum?

This was part of a lighting system on a floating dock where boats can be boarded for an ocean cruise, or taxi to the airport.


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2003
Posts: 394
B
Member
Judging from the condition of the GRC, I vote for massive corrosion.

Joined: Aug 2002
Posts: 1,081
T
Member
Is any of this listed for use in a corrosive environment, such as near salt water?

Is there such a special listing requirement?

[This message has been edited by ThinkGood (edited 10-21-2003).]

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Joe:
I'll have to cast a vote that the conduit was "pulled" out of the (probably) aluminum condulet. You said "floating dock"......someone possibly forgot to take that into consideration when they made-up the pipe. Movement, or possibly "contraction" due to the length of the run and the temp when it was installed can factor in also.

John


John
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Think Good:
Yes, there is PVC coated RGC for corrosive areas. It's a BEAR to work with!!

Sch 80 PVC, if otherwise suitable for the location is the preferred. That is, after checking the spec, plans, and assuring that it's otherwise approved for the intended install. And, you can't forget the expansion joints.

John


John
Joined: Jan 2004
Posts: 91
R
Member
two dissimilar metals causes galvanic action. is the use of penetrox (or its equivalent) be used and comply with code. as to the installation the lazy electrician probably crossthreaded the pipe and after one thread caught left it that way. I agree that plastibond or ocal should have been used and the condulets cost a fortune.