ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 269 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Oct 2000
Posts: 2,749
Member
[Linked Image from themeterguy.com]

Service raceway pulled away from meter socket enclosure.


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Gee: From the looks of it....
Go up on the roof, install a guy cable on the left side of the mast. Pull the mast back plumb; install a few straps on the conduit, and a few masonry anchors in the meter pan; done.

Now if the guy was installed, ar a "drop support"; the situation in the photo may not have occured.
The POCO here requires a guy, or an independent "drop support" for a service installation as pictured
John


John
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
My PoCo would want a 2-1/2" mast plus guying.

What's a "drop support"?


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Joined: Oct 2000
Posts: 2,749
Member
Quote
230.28 Service Masts as Supports.

Where a service mast is used for the support of service-drop conductors, it shall be of adequate strength or be supported by braces or guys to withstand safely the strain imposed by the service drop.

Where raceway-type service masts are used, all raceway fittings shall be identified for use with service masts.

Only power service-drop conductors shall be permitted to be attached to a service mast.

Where the service drop is secured to the mast, a guy wire may be installed to support the mast and provide adequate mechanical strength to support the service drop.

Communications conductors such as those for cable TV or telephone service are not permitted to be attached to the service mast.
www.necdirect.org

[This message has been edited by Joe Tedesco (edited 11-08-2002).]


Joe Tedesco, NEC Consultant
Joined: Oct 2002
Posts: 210
S
Member
Looks like a truck must have "grabbed" the drop.

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
66:
A "drop support" is an I beam, or a substantial wood beam (4x6 or larger) that the service drop from the pole is supported by. We have quite a few of these around here. Purpose is to provide adequate support for the drop, instead of the "mast"
BTW, 2 1/2" is minimum pipe size for masts here also.


John
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
For Allegheny Power, 2" Pipe is allowed if the Point of attachment is between 18" and 24" from the roof. Up to 48" it must be 2-1/2" Pipe (or larger) and after 48", it must be guyed. Don't remember the maximum height for a 2-1/2" guyed mast.

OK, drop support. I've seen 'em, just didn't know what they were called...

Thanks!

[This message has been edited by sparky66wv (edited 11-09-2002).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Joined: Apr 2001
Posts: 518
J
Member
I have photos of a similar situation that progressed to "arcs & sparks." I suspect the same cause here: a truck backed into it.