Bucket Used as Underground J-Box #103303
06/22/02 05:12 PM
06/22/02 05:12 PM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
This bucket was used as a junction box for some pole lights located at a hospital.

They needed power to supply an emergency entrance sign, so they notched the top of a 2 inch conduit, and then pulled the wires out to feed it!
[Linked Image]


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Bucket Used as Underground J-Box #103304
06/22/02 08:27 PM
06/22/02 08:27 PM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
I wonder what the maximum wire-fill would be for this ingenious junction box. I don't suppose the NEC has a table to cover it! [Linked Image]

Re: Bucket Used as Underground J-Box #103305
06/22/02 08:49 PM
06/22/02 08:49 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
It works out to 223 8-AWG THWNs for bucket fill; but reduce that to 118 for 2ΒΌ gallons of cooling water per NEC 967.229(c)II(1a)v7.

Re: Bucket Used as Underground J-Box #103306
06/22/02 09:46 PM
06/22/02 09:46 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Why didn't they remove a section of the 1.5" or 2" conduit and put two 90's on. This apears to be a quasite type box and in reality would not need an expensive divider installed. [Linked Image] If they were trying to seperate systems per 517.30(C) they crossed over anyways, not to mention being in the same raceway. The quasite box would have been legal if it were Normal, Critical, or Life Safety branches exclusively, or Normal and Equipment branches combined.

Roger



[This message has been edited by Roger (edited 06-22-2002).]

Re: Bucket Used as Underground J-Box #103307
06/24/02 07:43 AM
06/24/02 07:43 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Aha!

After 4 days of searching, the new helper finally found that "bucket of amps".


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,849 Are you busy
184,205 Re: Forum
173,446 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.003s) Memory: 0.9681 MB (Peak: 1.1078 MB) Zlib enabled. Server Time: 2018-05-21 09:09:29 UTC