Why didn't they remove a section of the 1.5" or 2" conduit and put two 90's on. This apears to be a quasite type box and in reality would not need an expensive divider installed.
If they were trying to seperate systems per 517.30(C) they crossed over anyways, not to mention being in the same raceway. The quasite box would have been legal if it were Normal, Critical, or Life Safety branches exclusively, or Normal and Equipment branches combined.
Roger