This bucket was used as a junction box for some pole lights located at a hospital.

They needed power to supply an emergency entrance sign, so they notched the top of a 2 inch conduit, and then pulled the wires out to feed it!
[Linked Image]


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Aug 2001
Posts: 7,520
P
Member
I wonder what the maximum wire-fill would be for this ingenious junction box. I don't suppose the NEC has a table to cover it! [Linked Image]

Joined: Apr 2002
Posts: 2,527
B
Moderator
It works out to 223 8-AWG THWNs for bucket fill; but reduce that to 118 for 2ΒΌ gallons of cooling water per NEC 967.229(c)II(1a)v7.

Joined: May 2002
Posts: 1,716
R
Member
Why didn't they remove a section of the 1.5" or 2" conduit and put two 90's on. This apears to be a quasite type box and in reality would not need an expensive divider installed. [Linked Image] If they were trying to seperate systems per 517.30(C) they crossed over anyways, not to mention being in the same raceway. The quasite box would have been legal if it were Normal, Critical, or Life Safety branches exclusively, or Normal and Equipment branches combined.

Roger



[This message has been edited by Roger (edited 06-22-2002).]

Joined: Mar 2001
Posts: 2,056
R
Member
Aha!

After 4 days of searching, the new helper finally found that "bucket of amps".


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 70
Joined: January 2002
Top Posters(30 Days)
NORCAL 5
Trumpy 3
Popular Topics(Views)
300,300 Are you busy
229,978 Re: Forum
214,792 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5