ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
New tool
by gfretwell - 10/19/20 03:43 PM
Where is Everyone?
by Bill Addiss - 10/17/20 07:04 PM
Beyond Belief
by gfretwell - 09/27/20 12:03 AM
Questioning the electrical norms
by LongRunner - 09/23/20 06:38 AM
New in the Gallery:
Facebook follies, bad wiring
FPE in Germany pt.2
Who's Online Now
0 registered members (), 17 guests, and 16 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Surge Arresters. NEC 280 #10327 06/06/02 09:02 AM
Joined: Jul 2001
Posts: 311
F
Frank Cinker Offline OP
Member
Beyond voltage, frequency etc. how are surge arresters sized? The surge arrester will be connected to the service conductors. For this example, would the same size surge arrester be used for a 120/240V, single phase, 100 amp service or for a 120/240V, single phase, 400 amp service?

Frank

Work Gear for Electricians and the Trades
Re: Surge Arresters. NEC 280 #10328 06/06/02 08:39 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
Frank,
just speculation here, but i would venture that arrestors be sized in accordance to problems external...
It should be given some thought, for the sake of $400 +- of AFCI's in a panel here.

Re: Surge Arresters. NEC 280 #10329 06/06/02 09:23 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
Many Things to keep in mind.
Voltage ratings
Type of protection (Catagory A = low, B = Medium, C = high exposure to intense surges)
Breif explanation: http://www.currenttechnology.com/paper_2.htm
Good examples and info: http://www.currenttechnology.com/tutorial1.htm

Generally the device does not have an ampere rating because they are conencted in parallel to the protected conductors/equipment.

[This message has been edited by Ron (edited 06-06-2002).]


Ron
Re: Surge Arresters. NEC 280 #10330 06/06/02 11:42 PM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
One aspect that seems to get glossed over is the critical minimization of inductive reactance in conductors between the ‘magic black box’ and bus taps. A three-foot run of #4s severely limits the arrestor’s capability to clamp voltage AT THE 400A BUS. Basic laws of physics are often ignored.

Re: Surge Arresters. NEC 280 #10331 06/07/02 08:08 AM
Joined: Jul 2001
Posts: 311
F
Frank Cinker Offline OP
Member
Thank you for replies. I'm not up on surge arrester technology. I'll need to study more. Good links. Over the last week or so we've had quite a few storms in Western Pennsysvania.

I had a discussion with my Supervisor concerning the possibility of installing surge arrerstors on line side of service disconnect and T.V.S.S. (Transient Voltage Surge Suppressors) on the load side of the service disconnect in several of our buildings.

Re: Surge Arresters. NEC 280 #10332 06/07/02 12:47 PM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
There are arrestor packages "listed for use as service equipment," but I'd be sure that the utility will buy into your plan before you show up at a customer’s site with heavy cardboard box in hand. Taps should ideally be installed downstream of the metering but before the servce disconnect. [That may involve breaking a seal, so keep the utility in the loop. It’s a bit embarrassing to have a customer without a day’s worth of power while a dispute is going on.]

It’s crucial to keep the tap conductors as short as possible. The arrestor guys may promise the world, but understand that those numbers can be made instantly worthless because they are based on tests at the arrestor terminals, and surge ratings will always be lower/slower at the other end of the tap.

This text and links are intended ONLY as an example. GE just seems to explain the problem fairly well. They differentiate the connection as “Tee-” versus “Series-connected.” http://www.geindustrial.com/products/applications/choose.pdf http://www.geindustrial.com/products/brochures/9l10f.pdf
GE hawks a true Kelvin-connected series, but they’re limited to a 100-ampere-continuous circuit rating. http://www.geindustrial.com/products/brochures/9l10m.pdf

The only time these comments would not apply is where a equipment company insisted on some blind installation of a ‘showpiece’ arrester to fulfill some mealymouthed insurance or warrantee clause, with no real concern that it had to work properly. That’s where the little blobs with a locknut and three-foot leads prove useful. (Too many arrestor salesguys proudly list Durro-Test in their resumes.)

Regional variations and local customs will determine how this applies to you.

Re: Surge Arresters. NEC 280 #10333 06/07/02 02:41 PM
Joined: Jul 2001
Posts: 311
F
Frank Cinker Offline OP
Member
Good advice which I will keep in mind.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,720 Are you busy
204,961 Re: Forum
193,065 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3