Yes, he actually threw a potato at me!
no respect ...what a potatohead![b[From 527-4(G)[/b]
(G) Splices. On construction sites, a box shall not be required for splices or junction connections where the circuit conductors are multiconductor cord or cable assemblies, provided that the equipment grounding continuity is maintained
with or without the box. See 110.14(B) and 400.9. A box, conduit body, or terminal fitting having a separately bushed hole for each conductor shall be used wherever a change is made to a conduit or tubing system or a metal-sheathed cable system.
an 02' change, welcome back the 'flying splice'
'supports' also.
all amendatory to chaps 1-3
( and i've been buying the 3-wire so temp stringers....)
also check out 527.4 (C) ex, NM & even single conductor seems kosher..no hieght limits
He does flunk the 'lampholder'bit in 527.4(F), maybe he'll wing one pitchin' veggies...