Lockout Requirements Changed in 2002 NEC #103024 03/08/02 06:07 PM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
[Linked Image]

http://www.bussmann.com/library/docs/430.102%20Disconnecting%20Means%20Location.pdf


[This message has been edited by Joe Tedesco (edited 08-10-2002).]


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Lockout Requirements Changed in 2002 NEC #103025 03/08/02 08:43 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
Joe,
While it is correct that the disconnecting means is required by the code to have a "permanently" installed locking device, if the equipment doesn't have such a device the service person is still permitted to install his or her own temporary device as a lockout. There are a number of devices on the market that can be installed on breaker boxes to provide the required permanent lockout means. Here ia a link to one such product: http://multimedia.mmm.com/mws/media...mp;tC9&MC9&&&HcKkbzzzzY-

Would you consider the devices that snap onto the breaker and are held in place by the panel cover a "permanent" means?
Don(resqcapt19)


Don(resqcapt19)
Re: Lockout Requirements Changed in 2002 NEC #103026 03/08/02 08:48 PM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
Don:

You raise a good question, and the pen should be put to the paper for a 2005 proposal.

None of the items you describe here are really "permanent" -- so that will be the question -- can they still be used?


Joe Tedesco, NEC Consultant
Re: Lockout Requirements Changed in 2002 NEC #103027 03/15/02 12:31 AM
Joined: Apr 2001
Posts: 518
J
John Steinke Offline
Member
I really hat it when manufacturers try to use/abuse the code to hawk their latest wares. If Bussman thinks that everybody is going to replace all their fuse boxes, motor disconnects, etc., they must have caught that Mississippi Mosquito virus!
NEC doesn't cover or address temporary or maintenance lockouts- that's a matter for OSHA. OSHA say USE THEM.
It should also be noted that new codes apply only to new installs- so older enclosures, even ones that lack padlock hasps, are still compliant (code at time of install applies)
We've come a long way in ten years; it wasn't so long ago that there were no lock-out devices for fuses and circuit breakers.
I admit to violating OSHA rules on a regular basis. For example, I have purchased my own, rather than relying on my employer to provide an adequate assortment. In doing so, I am violating OSHA rules, which forbid this. So cite me! I also use my toolbox lock for lock-out purposes- another violation! I will do whatever is necessary to protect myself, even if the rules say "no."
I have also used zip-ties to secure lock-out devices. Something about a brass padlock swinging around in a hot box, or somebody banging into a swinging door (that the lock keeps from closing) strikes me as silly.

Re: Lockout Requirements Changed in 2002 NEC #103028 03/15/02 07:51 PM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
The one on the bottom left of the "Unpermissable" ones is a good one.
Locks out everything from a snap switch to a big breaker. I guess I've got to throw it away?

Re: Lockout Requirements Changed in 2002 NEC #103029 03/15/02 09:02 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
John,
John,
Quote
NEC doesn't cover or address temporary or maintenance lockouts- that's a matter for OSHA. OSHA say USE THEM.
When a new installation is made for a motor circuit, the NEC in 430.102 requires that a permanent lockout device be provided as part of the equipment. It is a code violation to install a motor circuit disconnect that can only be locked out by the use of a temporary device. Temporary lockouts will still be required for existing disconnects and non-motor disconnects. Lock out/ tag out is a very important safety issue and we need to follow the rules.
Don(resqcapt19)


Don(resqcapt19)
Re: Lockout Requirements Changed in 2002 NEC #103030 03/16/02 10:34 PM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
Joe,

Most people don't realize how much this code will enforce. Doesn't this code mean that any well drilled in the front (back) lawn also needs a disconnect outside and within 50' and insight of the well head? How about ejector pumps? attic fans? any motor? etc? This can be far reaching if you think about it.

Harold


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The Watt Doctor
The Watt Doctor
Mont Belvieu, TX
Posts: 437
Joined: December 2001
Show All Member Profiles 
Top Posters(30 Days)
BigB 2
Popular Topics(Views)
270,998 Are you busy
205,003 Re: Forum
193,121 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3