Golf Clubhouse Violations! #103014 03/04/02 08:34 AM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
[Linked Image]

Submitted by: Kerry Johnson

"What's Wrong Here?"


[This message has been edited by Joe Tedesco (edited 03-04-2002).]


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Golf Clubhouse Violations! #103015 03/04/02 09:55 PM
Joined: Jan 2002
Posts: 122
W
wirewiz Offline
Member
Installer gets an "E" for effort! [Linked Image] Wouldn't it have taken less effort to spend 25 cents at the local hardware store for a nipple. As opposed to $10 in labor notching that piece of copper, or is it a copper raceway? I guess all this is support for properly trained and licensed personel!

Some NEC I see violated:
Top left
250-148
370-17B

Bottom left
370-29

Right
370-17B
110-12
What did I miss?

Re: Golf Clubhouse Violations! #103016 03/04/02 10:04 PM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
Great calls wirewiz

I would also call 99 or 02 NEC Section 300-14. last sentence for lower left.

" .... Where the opening to an outlet, junction, or switch point is less than 200 mm (8 in.) in any dimension, each conductor shall be long enough to extend at least 75 mm (3 in.) outside the opening."

What else?

Does anyone have any additional references?


Joe Tedesco, NEC Consultant
Re: Golf Clubhouse Violations! #103017 03/04/02 10:38 PM
Joined: Jan 2002
Posts: 122
W
wirewiz Offline
Member
Thanks Joe
Would the top left require the same as 300-14? If the conductors were ever tapped there would not be 6 inches available from each point of entrance?

Re: Golf Clubhouse Violations! #103018 03/04/02 10:59 PM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
Yes, I agree and the issue would also come up when an extension ring was added.

That's what is behind the rule cited above. If the wires pass through unbroken, they are not required to meet the 6 inch rule. A proposal was sent in, and was rejected when an electrician asked that the length of the "loop" be 12 inches so as to avoid the problem with less than 6 inches.


Joe Tedesco, NEC Consultant
Re: Golf Clubhouse Violations! #103019 03/06/02 08:37 AM
Joined: Mar 2002
Posts: 2
J
John Eichorst Offline
Junior Member
Upper Left

After talking to Kerry. I learned that the conduit entering the back of the box stubbs through a block wall. Instead of comming straight into the box, it comes in at an odd angle. Therefore a connector wouldn't have been square to the box. That's propably when someone got the idea to notch the conduit and bend it over.

During the remodel this "system" was removed.

Re: Golf Clubhouse Violations! #103020 03/06/02 10:15 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
What is the voltage?
Would a bonding bushing be required for the broken concentric ring?

Re: Golf Clubhouse Violations! #103021 03/06/02 05:10 PM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
Redsy:

If this was service equipment supplied at any typical building supply voltage, the code would call for bonding bushings where their were concentric or eccentric rings still present, and when the voltage is over 250 volts to ground the bonding could only be accomplished in the same manner for services. See 2002 NEC 250.97

We should also remember that so-called "donuts" are not going to satisfy the bonding requirements - they are only used to correct a mistake!


Joe Tedesco, NEC Consultant
Re: Golf Clubhouse Violations! #103022 03/06/02 07:27 PM
Joined: Mar 2002
Posts: 2
J
John Eichorst Offline
Junior Member
Voltage at the broken knockout is 208V 3P. It is branch circuit wiring feeding a HVAC condensing unit. Does it need a bonding bushing? If the knockout was still intact, would a bonding bushing required?

Re: Golf Clubhouse Violations! #103023 03/06/02 09:23 PM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
John:

No, because the voltage to ground is not over 250 volts, but a bushing that will conform to 300.4(F) would be required.


Joe Tedesco, NEC Consultant

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
NORCAL 3
Popular Topics(Views)
269,931 Are you busy
204,358 Re: Forum
192,577 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3