What's Wrong Here? #102988
01/18/02 11:11 AM
01/18/02 11:11 AM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Use the 2002 NEC to provide a specific code section reference list of what you see wrong here and how you would write a violation notice.

[Linked Image]


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: What's Wrong Here? #102989
01/18/02 03:39 PM
01/18/02 03:39 PM
T
Texas_Ranger  Offline
Member
Joined: Dec 2001
Posts: 2,428
Vienna, Austria
Looks like phone and network wiring, isn't it?
Or did I overlook something?
My thoughts would be lack of support and too many wires.

Re: What's Wrong Here? #102990
01/18/02 04:45 PM
01/18/02 04:45 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
800.5 and 800.6

Don(resqcapt19)


Don(resqcapt19)
Re: What's Wrong Here? #102991
01/19/02 08:24 AM
01/19/02 08:24 AM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
800.5 Access to Electrical Equipment Behind Panels Designed to Allow Access.

Access to electrical equipment shall not be denied by an accumulation of wires and cables that prevents removal of panels, including suspended ceiling panels.

800.6 Mechanical Execution of Work.
Communications circuits and equipment shall be installed in a neat and workmanlike manner.

Cables installed exposed on the outer surface of ceiling and sidewalls shall be supported by the structural components of the building structure in such a manner that the cable is not be damaged by normal building use.

Such cables shall be attached to structural components by straps, staples, hangers, or similar fittings designed and installed so as not to damage the cable.

The installation shall also conform with 300.4(D).


Joe Tedesco, NEC Consultant
Re: What's Wrong Here? #102992
01/25/02 11:20 PM
01/25/02 11:20 PM
M
mokern  Offline
Junior Member
Joined: Jan 2002
Posts: 1
La Crosse, WI, USA
Looks just like most of the computer closets at the university here...the network administrators just give blank looks when you casually mention codes...

Re: What's Wrong Here? #102993
01/26/02 08:49 PM
01/26/02 08:49 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,274
Fullerton, CA USA
300.11(A) [in part]
... "Cables and raceways shall not be supported by ceiling grids"

Re: What's Wrong Here? #102994
01/26/02 10:36 PM
01/26/02 10:36 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
electure,
Per 90-3 Chapter 8 stands alone, so 300.11(A) doesn't apply to this installation. I don't see this rule in Article 800.
Don(resqcapt19)


Don(resqcapt19)
Re: What's Wrong Here? #102995
01/28/02 08:42 PM
01/28/02 08:42 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,274
Fullerton, CA USA
Thanks, Don.
For some reason I thought that the "loophole" had been closed with '02.
I see not [Linked Image]

Re: What's Wrong Here? #102996
01/31/02 05:48 PM
01/31/02 05:48 PM
J
jcm20  Offline
Junior Member
Joined: Jan 2002
Posts: 1
NH
It wouldn't be the fact that the computer lines are tyewraped to the armored cable in the ceiling would it? It is ugly but I have seen much worse.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 4
Popular Topics(Views)
249,447 Are you busy
187,361 Re: Forum
176,700 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.003s) Memory: 1.0009 MB (Peak: 1.1694 MB) Zlib enabled. Server Time: 2018-09-25 03:14:56 UTC