#102988 01/18/02 10:11 AM
Joined: Oct 2000
Posts: 2,749
Member
Use the 2002 NEC to provide a specific code section reference list of what you see wrong here and how you would write a violation notice.

[Linked Image]


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#102989 01/18/02 02:39 PM
Joined: Dec 2001
Posts: 2,498
T
Member
Looks like phone and network wiring, isn't it?
Or did I overlook something?
My thoughts would be lack of support and too many wires.

#102990 01/18/02 03:45 PM
Joined: Nov 2000
Posts: 2,148
R
Member
800.5 and 800.6

Don(resqcapt19)


Don(resqcapt19)
#102991 01/19/02 07:24 AM
Joined: Oct 2000
Posts: 2,749
Member
800.5 Access to Electrical Equipment Behind Panels Designed to Allow Access.

Access to electrical equipment shall not be denied by an accumulation of wires and cables that prevents removal of panels, including suspended ceiling panels.

800.6 Mechanical Execution of Work.
Communications circuits and equipment shall be installed in a neat and workmanlike manner.

Cables installed exposed on the outer surface of ceiling and sidewalls shall be supported by the structural components of the building structure in such a manner that the cable is not be damaged by normal building use.

Such cables shall be attached to structural components by straps, staples, hangers, or similar fittings designed and installed so as not to damage the cable.

The installation shall also conform with 300.4(D).


Joe Tedesco, NEC Consultant
#102992 01/25/02 10:20 PM
Joined: Jan 2002
Posts: 1
M
Junior Member
Looks just like most of the computer closets at the university here...the network administrators just give blank looks when you casually mention codes...

#102993 01/26/02 07:49 PM
Joined: Dec 2000
Posts: 4,291
Member
300.11(A) [in part]
... "Cables and raceways shall not be supported by ceiling grids"

#102994 01/26/02 09:36 PM
Joined: Nov 2000
Posts: 2,148
R
Member
electure,
Per 90-3 Chapter 8 stands alone, so 300.11(A) doesn't apply to this installation. I don't see this rule in Article 800.
Don(resqcapt19)


Don(resqcapt19)
#102995 01/28/02 07:42 PM
Joined: Dec 2000
Posts: 4,291
Member
Thanks, Don.
For some reason I thought that the "loophole" had been closed with '02.
I see not [Linked Image]

#102996 01/31/02 04:48 PM
Joined: Jan 2002
Posts: 1
J
Junior Member
It wouldn't be the fact that the computer lines are tyewraped to the armored cable in the ceiling would it? It is ugly but I have seen much worse.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 70
Joined: January 2002
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,559 Are you busy
231,909 Re: Forum
216,544 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5