JB in Electrical Vault #102861
02/12/07 09:24 PM
02/12/07 09:24 PM
C
Cinner  Offline OP
Member
Joined: Dec 2004
Posts: 78
Kelowna, B.C., Canada
Is it mandatory to have 1 metre clearance from the front of a JB that is mounted on the ceiling in an electrical room? The JB has 3/0 in and out that are spliced. Is it O.K. to have less than one metre if it is located above the switchgear?

Tools for Electricians:
Re: JB in Electrical Vault #102862
02/12/07 09:41 PM
02/12/07 09:41 PM
R
RobbieD  Offline
Member
Joined: Feb 2003
Posts: 231
Canada
Accessibility of Junction Boxes

CEC 12-3014 (2)

A vertical space of 900mm or more shall be required to provide ready access.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
244,048 Are you busy
181,039 Re: Forum
171,281 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.010s Queries: 14 (0.003s) Memory: 0.9410 MB (Peak: 1.0581 MB) Zlib enabled. Server Time: 2018-02-22 02:44:40 UTC