#102861 02/12/07 10:24 PM
Joined: Dec 2004
Posts: 78
C
Cinner Offline OP
Member
Is it mandatory to have 1 metre clearance from the front of a JB that is mounted on the ceiling in an electrical room? The JB has 3/0 in and out that are spliced. Is it O.K. to have less than one metre if it is located above the switchgear?

#102862 02/12/07 10:41 PM
Joined: Feb 2003
Posts: 231
R
Member
Accessibility of Junction Boxes

CEC 12-3014 (2)

A vertical space of 900mm or more shall be required to provide ready access.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Top Posters(30 Days)
triple 2
BigB 1
Popular Topics(Views)
304,938 Are you busy
233,352 Re: Forum
218,073 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5