JB in Electrical Vault #102861 02/12/07 10:24 PM
Joined: Dec 2004
Posts: 78
C
Cinner Offline OP
Member
Is it mandatory to have 1 metre clearance from the front of a JB that is mounted on the ceiling in an electrical room? The JB has 3/0 in and out that are spliced. Is it O.K. to have less than one metre if it is located above the switchgear?

Tools for Electricians:
Re: JB in Electrical Vault #102862 02/12/07 10:41 PM
Joined: Feb 2003
Posts: 231
R
RobbieD Offline
Member
Accessibility of Junction Boxes

CEC 12-3014 (2)

A vertical space of 900mm or more shall be required to provide ready access.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
BigB 4
Popular Topics(Views)
266,182 Are you busy
201,017 Re: Forum
189,705 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3