JB in Electrical Vault #102861
02/12/07 10:24 PM
02/12/07 10:24 PM
C
Cinner  Offline OP
Member
Joined: Dec 2004
Posts: 78
Kelowna, B.C., Canada
Is it mandatory to have 1 metre clearance from the front of a JB that is mounted on the ceiling in an electrical room? The JB has 3/0 in and out that are spliced. Is it O.K. to have less than one metre if it is located above the switchgear?

Tools for Electricians:
Re: JB in Electrical Vault #102862
02/12/07 10:41 PM
02/12/07 10:41 PM
R
RobbieD  Offline
Member
Joined: Feb 2003
Posts: 231
Canada
Accessibility of Junction Boxes

CEC 12-3014 (2)

A vertical space of 900mm or more shall be required to provide ready access.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,633 Are you busy
186,373 Re: Forum
175,849 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 14 (0.004s) Memory: 0.9418 MB (Peak: 1.0591 MB) Zlib enabled. Server Time: 2018-08-20 01:09:01 UTC