ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (CoolWill), 250 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Dec 2004
Posts: 78
C
Cinner Offline OP
Member
Does a 347 volt switch need to be marked "347v" on the cover plate?

What code rule states the answer?

Joined: Feb 2003
Posts: 231
R
Member
I would say no. There is no reference to it in the code book.
It is good practice to install a cover that says 347 though, it gives a heads up to whoever is working on it.

They make stainless steel flush switch covers that have 347 stamped on them and I think that they make them for FS boxes as well. I don't think that they make them for regular surface mounted boxes though.

Joined: May 2001
Posts: 378
F
Member
Ditto on RobbieD reply.

[This message has been edited by frank (edited 11-02-2006).]

Joined: Apr 2006
Posts: 31
M
Member
I've been told that it must be identified on all related objects - covers - to ensure the person peforming any repairs is aware of the hazzard. CEC 2006 30-308 (4)(b)

Joined: Feb 2003
Posts: 231
R
Member
Marsbar, your reference is to the integral disconnecting means that is now required in each flourescent fixture that is supplied by voltages exceeding 150V to ground. That rule is not talking about the light switch that Cinner is refering to.

Whoever told you that is wise because safety is key but it is not required and there is no code rule.

Joined: Jul 2005
Posts: 183
J
Member
To RobbieD, what is this integral disconnecting means on fixtures over 150v?
Do you know the rule number, and is there inexpensive disonnects now available rated for this voltage? thanks

Joined: Feb 2003
Posts: 231
R
Member
The new rule only applies to new fluorescent fixtures that are supplied by voltages exceeding 150 Volts to ground. I never saw one yet because I have only worked on older fixtures and never had to install a new one this year.

Look at 2006 CEC -

Rule 30-308
(4)Each fluorescent luminaire installed on branch circuits with voltages exceeding 150 volts-to-ground shall be:
(a) provided with a disconnecting means integral with the luminaire that simulataneously opens all circuit conductors between the branch circuit conductors and the conductors supplying the ballast(s); and
(b) marked in a conspicuous, legible, and permenant manner adjacent to the disconnecting means, identifying the specific purpose.

The description of the integral disconnect I guess could be anything, switch, plug, just as long as it does what the rule says.

Wish I could give you a picture of one but I never saw one.

I would say that they would not be able to sell 347V fixtures in Canada without one anymore because it has to meet the CSA standard. Since the CSA wrote the code book you would think that they updated their CSA Standard on the fixtures.

Hope this helps.

Joined: Jul 2005
Posts: 183
J
Member
thanks for the info RobbieD. We havent adopted the 2006 book yet in BC to my knowledge, but I work with lots of 347 volt flourescent lighting and this is very useful to know.

Joined: Apr 2006
Posts: 31
M
Member
CEC 2006 12-3002 Outlet box covers "cover plates installed on flush mounted and surface mounted outlet boxes shall be a type for which each is designed." A 347v switch is longer than a standard switch and would require a 347 box and cover plate. our ESA rep. mentioned that it may be added to the code as the number of accidents that occur. You are correct RobbieD.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5