C
CRM Offline OP
Member
The Alberta Building Code requires the principal exhaust fan to be interlocked with the furnace fan. An average size home usually has 2 bathroom fans upstairs, 1 downstairs. How do I determine what is the principal exhaust fan? Do I have to interlock all the bathroom fans with the furnace. On some newer homes I've seen there is a switch in the hallway, that somehow is wired in with the fan and furnace. What is the correct way to wire the fan and furnace in a new home. Thanks for any replies.

Horizontal Ad
Joined: May 2003
Posts: 1,157
Member
This is about all i can help you with [Linked Image] http://www.bcelectrician.com/furnace_fan_timer.html

Joined: Jul 2004
Posts: 787
L
Member
Doug, do I understand this right? When the "principal exhaust fan" is switched on, the furnace fan must also come on. It is assumed that the furnace also supplies make up air.

LarryC

Joined: Oct 2003
Posts: 147
C
Member
The Alberta Building Code does not say which exhaust fan must be used as the principle exhaust fan (it can be any exhaust fan in the home except the range hood fan). However the fan must have sufficient capacity to provide 50% of the total ventilation requirements of the home (ABC 9.32.3.4.(1)). And the switch must be centrally located (ABC 9.32.3.4(4)). Also two or more exhaust fans may be interlocked together so that they function simultaneously as the principal exhaust fan (ABC 9.32.3.4.(3)).

[This message has been edited by crash (edited 06-27-2006).]

[This message has been edited by crash (edited 06-27-2006).]


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Top Posters(30 Days)
Admin 3
CSS 1
Popular Topics(Views)
365,216 Are you busy
288,095 Re: Forum
266,777 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5