#102557 - 06/01/06 12:49 PM Service disconects for outbuildings  
Jonno  Offline
Member
Joined: May 2006
Posts: 20
I was working on a cottage recently, adding a few new circuits for a sump pump and washing machine and cleaning up some one else’s creative wiring.

The cottage has a detached shed, fed by a 3 conductor TEK, the original installer fed the TEK off of the living room lighting circuit, one of the conductors was a supply for the inside lights and plug, another was used as a switch leg so that the outside light on the shed was controlled by a switch in the living room. There is of course a neutral and EGC.

I moved the shed onto its own breaker. I was wondering on what everyone’s thoughts on how I could cover the service disconnect for this shed.


Tools for Electricians:

#102558 - 06/02/06 12:07 AM Re: Service disconects for outbuildings  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
not sure what you mean by "cover the service disconnect for this shed"


#102559 - 06/02/06 10:08 AM Re: Service disconects for outbuildings  
Jonno  Offline
Member
Joined: May 2006
Posts: 20
Sorry, my poor choice of wording.

I am asking for insight on how you would provide a service disconect for this shed.


#102560 - 06/05/06 12:11 AM Re: Service disconects for outbuildings  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
You would not really have a service disconnect to an outbuilding,since what you are describing is a branch circuit off your main panel. What you may require, depending on how much power you are bringing to the outbuilding, could be some kind of sub-panel. Be sure to read CEC 10-208. You are allowed two 15 amp circuits to the outbuilding without a subpanel-but I cant find that rule, be sure to talk to your local AHJ to check local rules also.


#102561 - 06/16/06 11:05 AM Re: Service disconects for outbuildings  
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
I would look at this in two ways. If it is a home there would be no requirement for a disconnect at the shed and I might prefer to see a sub panel I cannot think of any reason that a person would be required to run a sub panel and feed the circuits from their.
Even a commercial application if the shed is not a seperate tennant then it could still be fed either via a sub panel or separate circuits. Now if the shed was functionally seperate IE a different tennant then a panel with a local disconnect would be in order.
In BC each occupancy must have a local disconnect within the occupancy.


#102562 - 06/21/06 08:44 PM Re: Service disconects for outbuildings  
Cosimo  Offline
Junior Member
Joined: Jun 2006
Posts: 6
In Ontario this rule applies:
14-418 Disconnecting Means

(1) A single disconnecting means shall be provided either integral with or adjacent to the distribution equipment:

(a) Within each unit of a multi-unit building, other than a dwelling unit;

(b) Within each area common to more than one building, such as an underground parking area; or

(c) Within each building when fed from another building.

(2) Subrule (1) does not apply to circuits from part of fire alarm, fire protection and emergency systems.



Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7767 MB (Peak: 0.9230 MB) Zlib enabled. Server Time: 2017-12-15 19:53:32 UTC