I was working on a cottage recently, adding a few new circuits for a sump pump and washing machine and cleaning up some one else’s creative wiring.

The cottage has a detached shed, fed by a 3 conductor TEK, the original installer fed the TEK off of the living room lighting circuit, one of the conductors was a supply for the inside lights and plug, another was used as a switch leg so that the outside light on the shed was controlled by a switch in the living room. There is of course a neutral and EGC.

I moved the shed onto its own breaker. I was wondering on what everyone’s thoughts on how I could cover the service disconnect for this shed.

Tools for Electricians:
Re: Service disconects for outbuildings #102558
06/02/06 12:07 AM
06/02/06 12:07 AM
J
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
not sure what you mean by "cover the service disconnect for this shed"

Re: Service disconects for outbuildings #102559
06/02/06 10:08 AM
06/02/06 10:08 AM
J
Jonno  Offline OP
Member
Joined: May 2006
Posts: 20
Sorry, my poor choice of wording.

I am asking for insight on how you would provide a service disconect for this shed.

Re: Service disconects for outbuildings #102560
06/05/06 12:11 AM
06/05/06 12:11 AM
J
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
You would not really have a service disconnect to an outbuilding,since what you are describing is a branch circuit off your main panel. What you may require, depending on how much power you are bringing to the outbuilding, could be some kind of sub-panel. Be sure to read CEC 10-208. You are allowed two 15 amp circuits to the outbuilding without a subpanel-but I cant find that rule, be sure to talk to your local AHJ to check local rules also.

Re: Service disconects for outbuildings #102561
06/16/06 11:05 AM
06/16/06 11:05 AM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
I would look at this in two ways. If it is a home there would be no requirement for a disconnect at the shed and I might prefer to see a sub panel I cannot think of any reason that a person would be required to run a sub panel and feed the circuits from their.
Even a commercial application if the shed is not a seperate tennant then it could still be fed either via a sub panel or separate circuits. Now if the shed was functionally seperate IE a different tennant then a panel with a local disconnect would be in order.
In BC each occupancy must have a local disconnect within the occupancy.

Re: Service disconects for outbuildings #102562
06/21/06 08:44 PM
06/21/06 08:44 PM
C
Cosimo  Offline
Junior Member
Joined: Jun 2006
Posts: 6
In Ontario this rule applies:
14-418 Disconnecting Means

(1) A single disconnecting means shall be provided either integral with or adjacent to the distribution equipment:

(a) Within each unit of a multi-unit building, other than a dwelling unit;

(b) Within each area common to more than one building, such as an underground parking area; or

(c) Within each building when fed from another building.

(2) Subrule (1) does not apply to circuits from part of fire alarm, fire protection and emergency systems.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
andey 3
Popular Topics(Views)
253,199 Are you busy
189,862 Re: Forum
179,560 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 14 (0.003s) Memory: 0.9760 MB (Peak: 1.1207 MB) Zlib enabled. Server Time: 2019-02-16 05:26:15 UTC