Cable under a roadway #102259
12/13/05 11:48 PM
12/13/05 11:48 PM
C
Cinner  Offline OP
Member
Joined: Dec 2004
Posts: 78
Kelowna, B.C., Canada
How deep would you have to bury a 5000 volt acwu cable under a roadway. Does anyone know what section or rule pertains to this in the cec?

Tools for Electricians:
Re: Cable under a roadway #102260
12/14/05 03:18 PM
12/14/05 03:18 PM
dougwells  Offline

Member
Joined: May 2003
Posts: 1,143
kamloops BC Canada
Section 36 deals with HV installations but I can only see where it mentions in a building , not underground distribution at all. But it says it has to be marked every 3 meters

Re: Cable under a roadway #102261
12/14/05 08:50 PM
12/14/05 08:50 PM
Y
YORKIE  Offline
Member
Joined: Nov 2005
Posts: 20
abbotsford.bc
Section 12
Rule 12-012 Appendix B and table 53.This says 1000mm. If you have any doubts check with your local inspector

Re: Cable under a roadway #102262
12/14/05 09:05 PM
12/14/05 09:05 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I don't know beans about the Canadian code... and I consider 480v to be "high voltage."

However, I suspect my local utility would require such a line to be buried at least 5 ft. deep, especially if there was no other protection (such as pipe).

Re: Cable under a roadway #102263
06/20/06 12:45 PM
06/20/06 12:45 PM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
From Table 53 conductors over 750 volts must be buried a minimum of 1 meter or 39 1/2 inches for the metrically challenged.
High voltage is over 750 volts so the 480 volts is "low" voltage.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,903 Are you busy
184,257 Re: Forum
173,496 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.004s) Memory: 0.9666 MB (Peak: 1.1053 MB) Zlib enabled. Server Time: 2018-05-25 11:07:07 UTC