Storage shed receptacle #10222 06/02/02 07:54 AM
Joined: Jul 2001
Posts: 311
F
Frank Cinker Offline OP
Member
I believe it would be Code compliant to run one underground branch circuit to a storage shed and install a duplex receptacle without driving a ground rod etc. The single branch circuit would of course include an equipment grounding conductor. Am I correct?

Work Gear for Electricians and the Trades
Re: Storage shed receptacle #10223 06/02/02 10:07 AM
Joined: Apr 2001
Posts: 507
G
golf junkie Offline
Member
yes

Re: Storage shed receptacle #10224 06/02/02 12:21 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
Frank,
Don't forget that 225.31 requires a disconnect at the shed. The exception to 225.38 permits the use of a "snap" switch as the disconnect.
Don


Don(resqcapt19)
Re: Storage shed receptacle #10225 06/02/02 07:02 PM
Joined: Jul 2001
Posts: 311
F
Frank Cinker Offline OP
Member
Thank you for replies. I wasn't aware of the disconnect rule Don. A snap switch is certainly easy enough.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,787 Are you busy
205,000 Re: Forum
193,115 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3