Joined: Oct 2003
Posts: 31
C
Clyde Offline OP
Member
I've recently run into a situation that I havn't thought about since my days as an apprentice.

I need to calculate the short circuit rating of a couple of machines that are not currantly approved for use in Canada. As part of the certification, they need to be labelled with voltage, FLA, hz, phase etc as well as short circuit ampacity.

These nachines have an electric motor, 120 volts, and some mechanics for a printing shop.

Can anyone tell me if there is a calculation available to complete this job.

Any help would be appreciated.

Joined: Jan 2003
Posts: 174
B
Member
I did a google search on " short circuit current rating approved method " and received alot of good results.

If this doesn't work out for you let me know and i will post some links, good luck.

Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
To label equipment with a short circuit rating, would be very dependent on the devices in the power path and how they were supported and manufactured. Then they would be tested at that rated current to ensure no catastrophic failure.


Ron
Joined: Oct 2003
Posts: 31
C
Clyde Offline OP
Member
Thanks guys.

I agree with you Ron. There does not seem to be an effective way of testing the motors without actually destroying them in the process.

I did do a google search and found detailed methods of rating transformers but no motors.

I talked to the ESA field inspector and he indicated that for small motors (3/4 hp and smaller) a 5 ka is generally accepted.

Thanks for your thoughts. Any more would be appreciated.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Top Posters(30 Days)
dsk 3
Popular Topics(Views)
297,646 Are you busy
228,450 Re: Forum
213,302 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5