#102107 02/12/05 05:34 PM
Joined: Oct 2003
Posts: 60
C
Charles Offline OP
Member
I'm only 17 years old, but I know more than most people about electricity and what is right and what is wrong.

My father bought the house we are currently living in last August. It was built in about 1994. We are in Nova Scotia, Canada.

There is a separate detached garage, 24' by 36', with a subpanel.

The cable going from the main service in the basement to the exterior wall has this on the side:

1995 ALCATEL CANADA WIRE #2 AWG/3 ALUM ACM CSA NMD90 XLPE CANADEX 300V FT1

On the exterior is a non-metallic conduit. About 2 inches above grade, the conduit stops and the cable continues underground. Is this cable listed for direct burial?

My father is convinced it's okay since a building inspector passed it when we moved in... I doubt he paid tons of attention to the electrical.

Don't get me wrong, it's a beautiful house, but it's the same house with Romex run to where a shed once was, exterior fixtures lacking boxes and BX run to a lamp post.

It worries me and I need to know if it is okay or not.

Joined: Feb 2004
Posts: 74
C
CRM Offline
Member
The keywords are NMD90, which is loomex. Table 19 of the CEC lists this cable for exposed wiring in dry or damp locations only. It is not approved for direct burial.

Joined: Nov 2004
Posts: 37
J
Member
Direct burial wire will say NMW or NMWU (Non-Metallic Wet) on it. That one is NMD (Non-Metallic Dry).

So you are correct.


Link Copied to Clipboard