#102074 12/09/04 03:03 PM
Joined: Oct 2003
Posts: 172
G
Member
I,m changing an old industriul unit into three lofts.I,m using the existing incoming 600v fusible disconnect which feeds a 225kva transformer which then feeds a 800amp metering section.My question is do I need a disco in between the transformer and metering board or does the 600v main disco cover this.

#102075 12/09/04 04:11 PM
Joined: May 2001
Posts: 144
T
Moderator
The main disconnect should be fine until you get to the 800-amp 208-volt splitter.

Then you will have to install disconnect switches for each separate service, with or without utility or check meters, for the different lofts.

Tony Moscioni
Electrical Inspector
Electrical Safety Authority

#102076 12/10/04 09:29 AM
Joined: Oct 2003
Posts: 172
G
Member
Thanks Tony thats what I thought.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Top Posters(30 Days)
Admin 10
Trumpy 8
Popular Topics(Views)
280,460 Are you busy
213,547 Re: Forum
200,418 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5