Marrettes in Panel #102040 10/17/04 09:43 AM
Joined: Feb 2003
Posts: 231
R
RobbieD Offline OP
Member
Is there any code rule that says that you can not use marrettes in panels? You know if the wire is too short. CEC 6-212(1) talks about conductors feeding through. I never use marrettes in panels because I make sure the wires are long enough but I am curious if there is a code rule not allowing this.

Tools for Electricians:
Re: Marrettes in Panel #102041 10/19/04 10:35 PM
Joined: May 2001
Posts: 376
F
frank Offline
Member
The code rule escapes me right now but yes for branch panels as long as cross sectional area does not exceed 40% or something like that.Marretts in control panels are not.Ive had inspectors offer to accept marretts as a solution where someone has landed more than one wire on breakers listed for only one wire.

Re: Marrettes in Panel #102042 10/20/04 10:04 AM
Joined: Oct 2004
Posts: 13
A
aspencade Offline
Member
Robbie:

I think you got the rule already. The same rule specifies that you cannot use the panel as a junction box. If you make a connection with a marrette then you are using it as a junction box.

Don

Re: Marrettes in Panel #102043 10/20/04 11:04 PM
Joined: May 2001
Posts: 376
F
frank Offline
Member
See rule 12-3034 (ii).Wiring Space in Enclosures.
It is allowed except it's 75% cross sectional area not 40%.A circuit that enters and exits an enclosure in one or more directons is the defenition of a j-box. 6-212(1)keeps separately derived systems seperate or that's how CCS inspectors rationalize it.

[This message has been edited by frank (edited 10-21-2004).]


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
272,071 Are you busy
205,961 Re: Forum
194,010 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3