#101866 11/06/03 10:31 PM
Joined: Oct 2003
Posts: 147
C
crash Offline OP
Member
I have 2 questions:
1. If a 5-20RA receptacle was installed in full 1complience of 26-710(b), and someone was to at another date plug into this circiut a "motor-only" applience (for example a vacuum cleaner), would this violate 28-200(b)?
2. If section 14 would allow a larger overcurrent device than section 28 the which size would you choose.

#101867 11/06/03 11:34 PM
Joined: May 2001
Posts: 144
T
Moderator
Crash,

A)No there would be no violation.

Rationale for Rule 28-200.

Because most motors have an inrush current approximately six times the motor full load current, the overcurrent device shall be of sufficient ampacity to avoid nuisance tripping.

Intent for Rule 28-200.

We intend to allow the trip values shown in Table D12, but if fuses are used and the percentage value in Table 29 will not allow the motor to start, this value may be increased. Table 26 reflects the values shown in Table 29 and is a handy guide. Appendix B provides guidance on sizing of the overcurrent protection.

B)Personally, The lower value.

#101868 11/08/03 04:34 PM
Joined: Oct 2003
Posts: 147
C
crash Offline OP
Member
Thanks, Tony.
I was thinking more along the line, that if the FLA was not known, or Table 29 indicated an over-current value of less than 14A. Then the notwithstanding clause in 28-200(b) would still allow this motor to be connected to a standard 15A receptacle supplied by a 15A O.C. . But what if a T-Slot receptacle and 20A O.C. were installed in lieu of the standard. 28-200(b) only specifies allows up to 15A.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Top Posters(30 Days)
Trumpy 10
Admin 10
Popular Topics(Views)
280,438 Are you busy
213,522 Re: Forum
200,401 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5