Dlabrenz,
SEE > > Table 19 (Canadian Electrical Code PartI)
Conditions of Use and Maximum Allowable Conductor Temperature of Wires and Cables Other Than Flexible Cords,Portable Power Cables, and Equipment Wires.
++++++++++++++++++++++++++++++++++++++++++++
SEE > > CSA Standard: CAN/CSA-C22.2 No. 131-M89 (R1994)
Type TECK 90 Cable
++++++++++++++++++++++++++++++++++++++++++++
SEE > > Canadian Electrical Code Rule: Rule 12-600 Armoured Cable Work Rules
Rules 12-602 to 12-618 apply only to armoured cable work.
Rationale and Intent for Rule 12-600.
Because of its flexibility, the armoured cable method may be used for concealed work, and where appearance is not a concern, it may be used for exposed work.
The metal armour sheath, made of either steel or aluminum strip, provides mechanical protection for the insulated conductors.
The cable armour or cables incorporating an internal copper or aluminum strip that is in contact with the armour does not constitute a bonding conductor (see Rule 10-510(2).)
Cables with aluminum armour have the letters “AL” indented or embossed in the armour.
Tony Moscioni
Electrical Inspector
Electrical Safety Authority