#101458 03/20/07 11:15 PM
Joined: Jan 2004
Posts: 1,507
G
Member
I'm trying to find a code article that would require a receptacle to serve the countertop of a wet bar located in the family room of a single family home.


George Little
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#101459 03/20/07 11:36 PM
Joined: Aug 2006
Posts: 356
Member
George,

If it is a stand alone unit it might fall under island category and it requires one.210-52(C)(2)

If it does not fall under the island category then i would say 210-52 (A)(2)(3) applies.

I like to know what others have to say.

Edward


Be kind to your neighbor, he knows where you live

#101460 03/21/07 01:02 AM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I don't think you will find anything that helps if this is not a kitchen, dining room or bathroom.
AS a design issue this should probably be a dedicated 20 but I fail to see a code requirement for any receptacles at a wet bar.
If they do put one in it has to be GFCI


Greg Fretwell
#101461 03/21/07 07:55 AM
Joined: Jan 2004
Posts: 1,507
G
Member
That's what I found too Greg. So if a person wanted to save a few bucks he could forgo the plug over the bar countertop. Save the cost of a GFCI outlet.


George Little
#101462 03/21/07 10:45 AM
Joined: Oct 2002
Posts: 482
Z
Member
I've always gone by 210.52 and it's various sub-sections, in the assumption that the wet-bar will require appliances such as blenders, etc., similar to a kitchen counter top. One circuit is usually acceptable however. GFCI protection on all outlets is definately a must.