Member
On the job I'm on, the smoke detectors in the HVAC ducts are powered from the convienience outlets in the RTU's. I don't have a copy of NFPA 72, but this doesn't seem like a good idea to me. Should any one trip or turn off a breaker for these outlets there is an alarm initiated. Any info will be appreciated.


Bill
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Apr 2004
Posts: 156
R
Member
I can't site a specific code but the equipment my company manufactures requires the entire smoke circuit to be operated off of a dedicated fire circuit. That includes the fire/smoke detectors, CO detectors, smoke purge and blower interlocks. If there is an outlet somebody is going to plug a drill into it eventually and depending on the fuse or circuit breaker size pop the circuit.

Edited out CO2 I must have been craving a soda.

Joined: Dec 2003
Posts: 751
E
Member
NFPA 72 requires:

"Fire alarm systems shall be provided with at least two independent and reliable power supplies, one primary and one secondary." and:

"Connections to the light and power service shall be on a dedicated branch circuit." and:

"The OC device shall have a red marking, shall be accessible only to authorized personnel, and shall be identified as 'FIRE ALARM CIRCUIT CONTROL'."


Earl
Joined: Dec 2003
Posts: 751
E
Member
Also, that would be CO detectors, not CO2.


Earl
Joined: Aug 2005
Posts: 214
E
Member
would a CO2 detector be what they use to track gases that cause global warming? j/k

Joined: May 2005
Posts: 984
Likes: 1
G
Member
CO is what they're concerned with; carbon monoxide is much more deadly than carbon dioxide (although they're both bad news in the appropriate concentrations).


Ghost307
Joined: Mar 2007
Posts: 25
M
Member
be sure the power source isn't gfi protected (760.21)


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Top Posters(30 Days)
Trumpy 6
NORCAL 3
Popular Topics(Views)
300,608 Are you busy
230,284 Re: Forum
215,066 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5