#101267 02/28/07 12:24 PM
Joined: Jan 2003
Posts: 59
C
ccdave Offline OP
Member
What code(s) prevent the use of extension cords for appliances, lamps etc. Please be as specific so as to convience this "lawyer" his refer. in his dining room must no be on a cord.. Thanks -dave

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#101268 02/28/07 12:34 PM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
Without starting an argument I think it is safe to say extension cords can NOT be used for fixed in place equipment. (the easy example is an orange cord running up to a garage door opener). Beyond that it starts geting hazy. The intent of 210.52(A) is to avoid extension cords but I am not sure how you stop the end user from extending a switched outlet around the wall to a lamp with a listed extension cord.


Greg Fretwell
#101269 02/28/07 12:49 PM
Joined: Mar 2005
Posts: 1,213
S
Member
590.3(B) restricts temporary cabling to a maximum of 90 days in this case.

400.8(1) is oft cited, as extension cords are most often used because there's no receptacle within 6' of where it should be. Also, the cords used are almost always too small- if you're using a cheap #18 extension cord on a 20A outlet, you're violating 400.5. As I work in a government office, they flat out forbade extension cords as illegal, and issued surge supressors with 12' cords instead! (Surge supressor is a device, which makes it not an extension cord, and therefore legal.) Letter the law vs intent of the law, I guess.

[This message has been edited by SteveFehr (edited 02-28-2007).]

[This message has been edited by SteveFehr (edited 02-28-2007).]

#101270 02/28/07 02:07 PM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I may have been involved in the issue Steve is talking about if these were the cords in computer rooms. The determining factor from the safety standpoint is these "approved" surge strips also provide overcurrent protection. It was determined that a strip with O/C protection and no surge protection would also be OK but the NEC specifically allowed the ones with surge protection


Greg Fretwell
#101271 02/28/07 03:05 PM
Joined: Feb 2002
Posts: 375
G
Member
Extension cords are legal.

In fact, they are made for just the purpose the person wishes to use them for.

#101272 03/01/07 12:49 PM
Joined: Jan 2003
Posts: 59
C
ccdave Offline OP
Member
Thank you! 400.8 was what I was looking for--dave

#101273 03/02/07 06:48 PM
Joined: Aug 2005
Posts: 4
H
Junior Member
Show him 210.52 (B)(1), then 400.8! If he doesn't get it then, he must really be my neighbor!

Hank