Are two circuit the max for a detached garage #101173
02/14/07 09:27 PM
02/14/07 09:27 PM
N
nov  Offline OP
Member
Joined: Aug 2004
Posts: 69
New Jersey
Are two circuit the max that I can get to a detached garage with out putting a sub panel in. I thought you can run a 12/3 and share the neutral to give you the two circuits is this correct.
thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: Are two circuit the max for a detached garage #101174
02/14/07 11:13 PM
02/14/07 11:13 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Quote
I thought you can run a 12/3 and share the neutral to give you the two circuits is this correct.

That is a single circuit...a multiwire circuit.
Quote
225.30 Number of Supplies
Where more than one building or other structure is on the same property and under single management, each additional building or other structure that is served by a branch circuit or feeder on the load side of the service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.

Don


Don(resqcapt19)
Re: Are two circuit the max for a detached garage #101175
02/15/07 12:49 AM
02/15/07 12:49 AM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
This is an excellent question and I've had to deal with it before. Someone wanted to run a multiwire branch circuit as Don discribed, for lights and plugs. In addition he wanted to run a circuit for a welder. I told him he needed to have a sub-panel and he had a fit. He ultimately put in a sub-panel but he was not happy. The multiwire branch circuit was one circuit but adding the welder was the second circuit.


George Little
Re: Are two circuit the max for a detached garage #101176
02/15/07 09:24 PM
02/15/07 09:24 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,289
Estero,Fl,usa
If the welder was using L/L on the same 15/20a MW circuit I would probably question the decision. If you are saying he ran a MW plus a welder circuit I agree 100%. With few exceptions you can only run one set of ungrounded conductors to another building.

In the single circuit situation you still want a disconnect ... ?


Greg Fretwell
Re: Are two circuit the max for a detached garage #101177
02/15/07 09:52 PM
02/15/07 09:52 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Greg- Not quite sure what you mean by "L/L" but for my case he ran a 20a. 120/240v. multiwire branch circuit and a 40a. 240v, welder circuit.


George Little

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,708
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
Popular Topics(Views)
249,378 Are you busy
187,310 Re: Forum
176,653 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 14 (0.003s) Memory: 0.9692 MB (Peak: 1.1076 MB) Zlib enabled. Server Time: 2018-09-22 21:07:19 UTC