Are two circuit the max for a detached garage #101173 02/14/07 08:27 PM
Joined: Aug 2004
Posts: 69
N
nov Offline OP
Member
Are two circuit the max that I can get to a detached garage with out putting a sub panel in. I thought you can run a 12/3 and share the neutral to give you the two circuits is this correct.
thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: Are two circuit the max for a detached garage #101174 02/14/07 10:13 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
Quote
I thought you can run a 12/3 and share the neutral to give you the two circuits is this correct.
That is a single circuit...a multiwire circuit.
Quote
225.30 Number of Supplies
Where more than one building or other structure is on the same property and under single management, each additional building or other structure that is served by a branch circuit or feeder on the load side of the service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.
Don


Don(resqcapt19)
Re: Are two circuit the max for a detached garage #101175 02/14/07 11:49 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
This is an excellent question and I've had to deal with it before. Someone wanted to run a multiwire branch circuit as Don discribed, for lights and plugs. In addition he wanted to run a circuit for a welder. I told him he needed to have a sub-panel and he had a fit. He ultimately put in a sub-panel but he was not happy. The multiwire branch circuit was one circuit but adding the welder was the second circuit.


George Little
Re: Are two circuit the max for a detached garage #101176 02/15/07 08:24 PM
Joined: Jul 2004
Posts: 9,558
G
gfretwell Online Content
Member
If the welder was using L/L on the same 15/20a MW circuit I would probably question the decision. If you are saying he ran a MW plus a welder circuit I agree 100%. With few exceptions you can only run one set of ungrounded conductors to another building.

In the single circuit situation you still want a disconnect ... ?


Greg Fretwell
Re: Are two circuit the max for a detached garage #101177 02/15/07 08:52 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
Greg- Not quite sure what you mean by "L/L" but for my case he ran a 20a. 120/240v. multiwire branch circuit and a 40a. 240v, welder circuit.


George Little

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 18
NORCAL 12
Popular Topics(Views)
274,154 Are you busy
207,958 Re: Forum
195,600 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3