ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Countertop Receptacles
by HotLine1 - 05/18/23 12:40 PM
Windows 10, who's upgraded?
by LindaParker - 05/15/23 04:29 AM
We can all breathe easy....
by gfretwell - 05/11/23 01:00 PM
What's your Hobby?
by gfretwell - 05/11/23 12:57 PM
Your favourite food?
by renosteinke - 05/10/23 09:28 PM
New in the Gallery:
Burger King crown sillyness
Burger King crown sillyness
by wa2ise, December 11
240/208 to a house
240/208 to a house
by wa2ise, October 9
Who's Online Now
0 members (), 55 guests, and 11 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#101113 02/09/07 05:56 PM
Joined: Jan 2007
Posts: 59
D
Member
If my nameplate on a residental outside ac unit says 20 amp min fuse,2o amp max fuse,13.6 running amps.....does that mean I could in theory pull a 14 home-run AND put it on a 20 breaker if I wanted to?

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#101114 02/09/07 07:01 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Probably yes. Even tho you might be terminating in a 60° terminal. Look at the name plate again because it seems strange to have the Min fuse of 20a. and the Max fuse as 20a. Unless I read your post incorrectly.


George Little
#101115 02/09/07 09:00 PM
Joined: Jun 2005
Posts: 821
S
Member
Yes, #14 THHN/ THWN could be used on an A/C Condensing Unit that requires a 13.6 minimum amperage rating based on article 240.4 (G). The overcurrent protective device (OCPD) should always be what the nameplate calls for based on 110.3 (B). It should also be noted that if the nameplate calls for 'MAX FUSE' then you'll need a fused disconnect. Those aren't as common as they used to be 20 years ago (or so they tell me).

#101116 02/10/07 12:49 PM
Joined: Jan 2007
Posts: 59
D
Member
Tks...I am wanting to make sure that this is one of the exceptions to 310.16 that allows you to alter from putting 14 only on a 15 amp breaker and so forth with the 12 and 10 wire

#101117 02/10/07 02:26 PM
Joined: Feb 2002
Posts: 840
C
Member
With the new federal regulations that mandate 13 SEER minimum efficiency, I am seeing a lot of AC's that only require a minimum circuit ampacity of 15 or 20.

Peter


Peter
#101118 02/15/07 10:26 AM
Joined: Jan 2007
Posts: 59
D
Member
I posted this topic a week or so ago and by coincidence,me and my helper were sent to another persons job(we've been slow lately) to change an AC feed.It is a remodel with 3 ACs,all new,using the exsisting feeds.Well,the AC in question had a no.10 pulled to it and the info on nameplate was as follows..23.9 min.ampacity,40min breaker,40 max breaker....could the no.10 have been used?

#101119 02/15/07 06:24 PM
Joined: Dec 2003
Posts: 751
E
Member
dilydaler,

440.6(A)tells us to size the conductors based on the nameplate rated load current. The exception says: "Where so marked, the branch-circuit selection current shall be used instead of the rated-load current to determine the rating or ampacity of the ....branch-circuit conductors..."

440.32 tells us to size the conductors at 125%.

Assuming your AC unit was not "so marked for branch-circuit selection current", then the #10s are good for the 23.9 x 1.25 = 29.875 amps.

The #10s could have been used, IMHO.


Earl
#101120 02/16/07 03:15 PM
Joined: Jun 2005
Posts: 821
S
Member
Quote
Well,the AC in question had a no.10 pulled to it and the info on nameplate was as follows..23.9 min.ampacity,40min breaker,40 max breaker....could the no.10 have been used?


Absolutely. The nameplate tells you all you need to know. The minimum ampacity, and the maximum breaker size.

#101121 02/16/07 03:25 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Quote
Tks...I am wanting to make sure that this is one of the exceptions to 310.16 that allows you to alter from putting 14 only on a 15 amp breaker and so forth with the 12 and 10 wire.

Actually, the restriction for limiting the protection for #14, 12, and 10 is not in table 310.16 it is in 240.4(D). But 240.4(D) is not applicable if you have one of the permissable loads in 240.4(G). Most motor and HVAC loads are covered by 240.4(G) and so they can use these size conductors at their maximum table 310.16 values (as restricted by the equipment terminations).


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Top Posters(30 Days)
Trumpy 11
Popular Topics(Views)
306,956 Are you busy
234,795 Re: Forum
219,134 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5