Table 310.15(B)(6) #101047
02/05/07 07:18 PM
02/05/07 07:18 PM
Tom  Offline OP
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
I'm taking an informal poll here.

Should the table apply to a feeder run from a dwelling to a detached shop?


Few things are harder to put up with than the annoyance of a good example.
2017 / 2014 NEC & Related Books and Study Guides
Re: Table 310.15(B)(6) #101048
02/05/07 07:28 PM
02/05/07 07:28 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,290
Estero,Fl,usa
No, it is only for the main feeder to the dwelling.


Greg Fretwell
Re: Table 310.15(B)(6) #101049
02/05/07 07:41 PM
02/05/07 07:41 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
The detached shop is not a dwelling unit so that table can not be used.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Table 310.15(B)(6) #101050
02/05/07 07:57 PM
02/05/07 07:57 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Another no here.

Roger

Re: Table 310.15(B)(6) #101051
02/05/07 09:53 PM
02/05/07 09:53 PM
S
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
No, it is only good for the main feeder and to other panels within the same dwelling. Conductors feeding a detached "shop" must comply with 310.16. So it's ok to run #4 copper feeders to a subpanel on the 2nd floor of a dwelling for 100 amps, but if 100 amps is desired for a detached shop, #2 copper should be run.

Re: Table 310.15(B)(6) #101052
02/05/07 10:55 PM
02/05/07 10:55 PM
S
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
That's kinda dumb ain't it?

Re: Table 310.15(B)(6) #101053
02/05/07 10:56 PM
02/05/07 10:56 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,290
Estero,Fl,usa
Shock, a sub panel is not a "main feeder" unless that is the source of all current to a dwelling. For example, if you had a 100a disconnect at ther meter feeding a distribution panel that would be a main feeder. If you come to a main panel with other loads and then feed another sub, that is not a main feeder and you us 310.16.


Greg Fretwell
Re: Table 310.15(B)(6) #101054
02/06/07 12:35 AM
02/06/07 12:35 AM
S
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
A main feeder, and all other feeders within the same dwelling, shall comply with Table 310.15(B)(6).

Re: Table 310.15(B)(6) #101055
02/06/07 12:46 AM
02/06/07 12:46 AM
C
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
Quote
A main feeder, and all other feeders within the same dwelling, shall comply with Table 310.15(B)(6).


Not sure where you are getting this from. 310.15(B)(6) can't be used for subpanels.

310.15(B) (6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders For individual dwelling units of one family, two-family, and multifamily dwellings, conductors, as listed in Table 310.15(B)(6), shall be permitted as 120/240-volt, 3-wire, single-phase service-entrance conductors, service lateral conductors, and feeder conductors that serve as the main power feeder to each dwelling unit and are installed in raceway or cable with or without an equipment grounding conductor. For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboards(s). The feeder conductors to a dwelling unit shall not be required to have an allowable ampacity rating greater than their service-entrance conductors. The grounded conductor shall be permitted to be smaller than the ungrounded conductors, provided the requirements of 215.2, 220.61, and 230.42 are met.

Curt


Curt Swartz
Re: Table 310.15(B)(6) #101056
02/06/07 03:57 AM
02/06/07 03:57 AM
S
stamcon  Offline
Member
Joined: Mar 2001
Posts: 330
So San Francisco CA
Quote
For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboards(s).


Isn't any panel located downstrem of the main disconnect a "subpanel"? Or does the main disconnect have to be an overcurrent device, to have any panel downstream a "subpanel"?

steve


Steve
Page 1 of 5 1 2 3 4 5

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Popular Topics(Views)
249,470 Are you busy
187,388 Re: Forum
176,728 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 15 (0.004s) Memory: 1.0287 MB (Peak: 1.2049 MB) Zlib enabled. Server Time: 2018-09-26 06:54:29 UTC