ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 265 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#100755 01/02/07 02:08 PM
Joined: Jan 2004
Posts: 1,507
G
Member
When you have an island counter with a sink in it that has counter space on each side of the sink- At what point does the island require more than one receptacle? Another way of putting it - At what point is the island sink creating two countertops? See 210.52(C)(4).


George Little
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#100756 01/02/07 03:44 PM
Joined: Dec 2003
Posts: 751
E
Member
When both side bars exceed 12 x 24 inches

[This message has been edited by earlydean (edited 01-02-2007).]


Earl
#100757 01/02/07 04:09 PM
Joined: Jun 2005
Posts: 821
S
Member
But if the island is on wheels....

#100758 01/02/07 04:36 PM
Joined: Dec 2003
Posts: 751
E
Member
Be sure to empty the bucket daily, and fill the tank on the top.


Earl
#100759 01/02/07 06:29 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Quote
When both side bars exceed 12 x 24 inches

So if the island is large and the left side and the right side of the sink are 36" x 36" each, do I require two receptacles on each side of the sink?


George Little
#100760 01/02/07 06:42 PM
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
George:
OK, 36" with a recept centered leaves 18" on each side. Based on that, two will do.

But, knowing you, this may be another trick question!

John


John
#100761 01/02/07 06:48 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Quote
George:
OK, 36" with a recept centered leaves 18" on each side. Based on that, two will do.
But, knowing you, this may be another trick question!

John
Why would you ever suspect me of being that way?

I'm merely trying to find out if I'd ever need more than 2 receptacles on an island counter. [Linked Image]


George Little
#100762 01/03/07 09:08 AM
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
George:
"Need" defined to NEC compliance would be two, as 'splained above.
"Need" as in the real world (design) or desires of the homeowner/customer are different animals.

As to the "trick".....I have a memory!

John


John
#100763 01/04/07 12:05 AM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
The way I read 210.52(C)(2) any counter "space" on an island 24" x 12" or greater it needs a receptacle. I see the counter space on each side of a sink as a separate space. The 24" is the troubling measurement. If the counter is only 23 inches across it has to be 24" long to trip this rule. If it is the regular 25" to 30" you see in an island the space only has to be 12" long.


Greg Fretwell