ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Ground Rods: Installation and Hook-Up
by renosteinke - 11/26/22 07:28 PM
Happy Thanksgiving all!
by Bill Addiss - 11/24/22 08:37 AM
Colt Firearms Switchbox
by sabrown - 11/22/22 01:33 PM
Perfect work light?
by gfretwell - 11/22/22 12:48 AM
copper prices where you live and inflation
by gfretwell - 11/21/22 01:52 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
1 members (Scott35), 54 guests, and 10 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#100603 12/04/06 08:25 AM
Joined: Apr 2002
Posts: 178
R
Member
Is there building codes or other issues with putting bell transformers in the attic space as long as there`s a pull down stair way making it accessible?Got red tagged last week. The one we use is edwards and it has a thermal cut out. The inspectors are sighting a safety concern with fire.

Thanks for some input.

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#100604 12/04/06 09:04 AM
Joined: Dec 2003
Posts: 751
E
Member
Transformers used with Class 2 or 3 circuits are exempt from the rules of Article 450 by 450.1 exception #4. Class 2 and 3 circuits are in parts I and III of Article 725. Section 725.51 covers the wiring on the supply side of the transformer. Did you violate something here? What do the installation instruction say about mounting this transformer? Is there a problem with excessive heat in this attic? Is your transformer marked with Class 2 or 3? Is the location of the cables or transformer subject to damage?
If the inspector cannot cite a specific code section you have violated, then there probably is not a violation.


Earl
#100605 12/04/06 09:32 AM
Joined: Mar 2005
Posts: 20
S
Member
The last transformer I installed listed on the box do not install in attics, maybe this is the red tag reason? As a side note I have also seen more doorbell transformers fail installed in attics then other areas.
Ron

#100606 12/04/06 11:35 PM
Joined: Nov 2005
Posts: 187
Member
Check out the Nutone # bk140slpb.


Hank
#100607 12/05/06 09:26 AM
Joined: Apr 2002
Posts: 178
R
Member
No everything good just they maintain it can`t go in the attic. maufact instructions don`t say I can`t and the xfmer has thermal cut out at 109c. Edwards is the one i`m using.We`re still hashing out the details for now he said it won`t hold up the CO but I need some verification for next time.

#100608 12/05/06 10:23 AM
Joined: Jan 2005
Posts: 5,360
Likes: 1
Cat Servant
Member
I seem to recall that there is such a rule, paseed in the last two code cycles... but I have not found it.

#100609 12/05/06 11:32 AM
Joined: Jul 2002
Posts: 717
M
Member
Quote"I seem to recall that there is such a rule, paseed in the last two code cycles... but I have not found it"

Reno, I don't remember any such change in the last two cycles, so my suggestion is don't look to hard for it.
This could be a local ammendment thing. My inspectors wanna see the instructions on the box if it is put into an attic or other confined space.

#100610 12/05/06 12:09 PM
Joined: Jan 2004
Posts: 1,507
G
Member
State of Michigan has a requirement that if you have a violation, the inspector or building official has to reference the code (law) you violated. Besides, I'd look rather stupid going into a court of law and try to convince 12 honest men/women that there was a violation and not be able to tell them which law they broke. duh!


George Little
#100611 12/05/06 08:54 PM
Joined: Jan 2005
Posts: 5,360
Likes: 1
Cat Servant
Member
Mike, If I know something for a fact, I'll say so. This thread deals with one of those trivial bits that I've never really had any involvement with, so my grasp of detail is pretty weak.

Yet, I would not dismiss the assertion out-of-hand; something sounded familiar. I'm still looking...

I did find that UL treats general-purpose transformers as though the terminations were rated for 60C. I can see where that van easily be exceeded in an attic.

As I said, this thread has me thinking, and looking.

And I agree; you don't 'cite' unless you CAN cite!


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,722
Joined: October 2000
Top Posters(30 Days)
Trumpy 3
NORCAL 3
Popular Topics(Views)
300,269 Are you busy
229,974 Re: Forum
214,790 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5