recepts in tub area #100364
11/15/06 05:59 PM
11/15/06 05:59 PM
S
Steve T  Offline OP
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
A homeowner wants to install a flat screen TV over a tub. There is about a one foot 'deck' area between the tub and the wall on which the TV will be installed apx. three or four feet above the tub water level. The TV needs a recept (behind the TV) for power.

This is tub only, not a shower.

Is this installation allowed?

2017 / 2014 NEC & Related Books and Study Guides
Re: recepts in tub area #100365
11/15/06 06:14 PM
11/15/06 06:14 PM
S
Steve T  Offline OP
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
680.71 would apply, I believe, and thus this installation is allowable as long as the TV manufacturer doesn't say the TV can't be in this area.

Sound good?

Re: recepts in tub area #100366
11/15/06 06:29 PM
11/15/06 06:29 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
No it does not sound good, it sounds incredibly bad and I would not do it for them.

Take a look at 406.8(C)


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: recepts in tub area #100367
11/15/06 06:42 PM
11/15/06 06:42 PM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Is it permissible to daisy-chain 3 GFCI receptacles in a row, just to make doubly/triply sure it's going to work?

Re: recepts in tub area #100368
11/15/06 07:22 PM
11/15/06 07:22 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Code wise you can daisy chain an infinite number of GFCIs.

You still can not put a receptacle in the tube area.

You also are not supposed to pass cords through walls.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: recepts in tub area #100369
11/15/06 10:13 PM
11/15/06 10:13 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Do we have a difinition of "tub area"? I've always understood "tub space" was the footprint of the tub or shower and up to the ceiling?
Edit to add the following comment: I see a lot of jobs where the deck around the tub is rather large and I've not had a problem with a receptacle in the tub "area" that I could quote a code section for a violation. Tough call. Always ask for GFCI protection. In the "tub or shower space" - no receptacles.

[This message has been edited by George Little (edited 11-15-2006).]


George Little
Re: recepts in tub area #100370
11/18/06 02:19 PM
11/18/06 02:19 PM
S
Steve T  Offline OP
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
680.71 clearly allows recepts less than five feet from the inside walls of the tub with GFCI protection. So the question is (as already said) what is the definition of 'tub area'? If it's the one, two, or three walls and ceiling that surround the tub, then would it be acceptable to put a recept just around the corner of a wall and run the cord around the wall and plug it in?

What about free standing tubs? What is that tub area?

Unfortunately, I think 680.71 throws a real kink in 406.8(C).

Re: recepts in tub area #100371
11/18/06 03:12 PM
11/18/06 03:12 PM
A
Alan Nadon  Offline
Member
Joined: Mar 2005
Posts: 399
Elkhart, IN. USA
680.71 is under the heading for hydromassage tubs.
All the general use electronic equipment I have seen has a warning to keep it away from water.
The only installation I ever saw that looked safe was where they built a closet at the end of the tub with a window into the bathroom. The T.V and receptacle were in the closet and the owner used a remote control. [Linked Image]
Alan--


Alan--
If it was easy, anyone could do it.
Re: recepts in tub area #100372
11/27/06 09:39 PM
11/27/06 09:39 PM
S
Steve T  Offline OP
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
What does keeping something 'away from water' mean?

Re: recepts in tub area #100373
11/27/06 09:44 PM
11/27/06 09:44 PM
S
Steve T  Offline OP
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
I think someone should propose similar wording from 410.4(D) for 406.8(C).

2011 here we come.

Page 1 of 4 1 2 3 4

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,086 Are you busy
185,526 Re: Forum
174,817 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.058s Queries: 15 (0.035s) Memory: 1.0275 MB (Peak: 1.2038 MB) Zlib enabled. Server Time: 2018-07-16 10:15:55 UTC