#100327 - 11/11/06 01:21 PM Pull Box v. Junction Box  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
If I have 2 inch conduit entering one side of a box and exiting with a 2 inch directly across from the conduit entering the box we have a straight pull. Right? If the conductors are AWG #4 or larger the box needs to be at least 16 inches between conduit entries hence at least a 16 inch box. (NEC 314.28(A)(1) '05 Ed.) Now- if I splice these conductors can I reduce the size of the box to 12 inches based on (2)?

Edited for spelling [Linked Image]

[This message has been edited by George Little (edited 11-11-2006).]


George Little

2017 / 2014 NEC & Related Books and Study Guides

#100328 - 11/11/06 02:36 PM Re: Pull Box v. Junction Box  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
George,
A splice doesn't change anything. If the conduit goes straight it is 8 X and if the conduit goes out a wall at 90° it is 6 X.
Don


Don(resqcapt19)

#100329 - 11/11/06 03:26 PM Re: Pull Box v. Junction Box  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Don- I agree with you put you'll get arguements if the conduits are offset or if there is a splice. I think it should be made clearer somehow. I ask for a 16 inch box.


George Little


Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.7521 MB (Peak: 0.8764 MB) Zlib enabled. Server Time: 2017-10-18 09:19:43 UTC