#100219 - 10/30/06 06:39 PM over 250 volts to ground  
luckyshadow  Offline
Member
Joined: Jan 2005
Posts: 307
Maryland USA
Question : Is a bonding bushing required when you have 277 volt wiring going through 1/2" liquidtight flexible metal conduit ( sealtight). This is terminated into a 4 square box that has concentric / eccentric knock outs. The knock outs are 1/2" to 3/4"
with only the 1/2" taken out.
I say yes a bonding bushing is required as per 250.97 another electrician say no you don't need them because its sealtight not a metal raceway like rigid conduit.


2017 / 2014 NEC & Related Books and Study Guides

#100220 - 10/30/06 06:58 PM Re: over 250 volts to ground  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
But LFMC is a metal raceway and in some cases can be used as the EGC. I've read 250.97 and 350.60 and 250.118 (C) and my educated guess would be YES, a bonding bushing is needed if this run is more than 6.'

I look forward to reading more replies on this matter but I have to leave for school now.


#100221 - 10/30/06 06:59 PM Re: over 250 volts to ground  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
IMHO you win the beer. Unless the box is listed to provide the required bonding with only the 1/2" ko removed. Some of them are.


George Little

#100222 - 10/30/06 07:01 PM Re: over 250 volts to ground  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I see it the same as George.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#100223 - 10/30/06 09:26 PM Re: over 250 volts to ground  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
OK, add a another agreement

John


John

#100224 - 10/31/06 10:22 AM Re: over 250 volts to ground  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
According to the UL white book, all outlet boxes (such as four inch) are suitable for bonding over 250 volts, without additional bonding, even with concentric.


Ryan Jackson,
Salt Lake City

#100225 - 10/31/06 04:27 PM Re: over 250 volts to ground  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Thanks Ryan, I thought I'd read that somewhere but I wasn't sure so I appreciate that info as does everyone else on this BB.


George Little

#100226 - 11/03/06 09:27 AM Re: over 250 volts to ground  
Elec N Spec  Offline
Member
Joined: Jul 2006
Posts: 33
Rochester Hills, MI USA
I was reading about the UL listing on the new MC/ap connectors and the fact that they are rated for use without a ground wire on boxes with both concentric and eccentric knock outs on UL listed boxes caught my eye. In some applications you do not have to bond as long as the box is approved



Member Spotlight
richard
richard
L.I. New York
Posts: 95
Joined: August 2003
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.601s Queries: 14 (0.588s) Memory: 0.7925 MB (Peak: 0.9527 MB) Zlib enabled. Server Time: 2017-10-24 11:34:35 UTC