ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Our Company!
by faradaygroup. 12/15/18 09:23 PM
Pull out fuse panel?
by wa2ise. 12/14/18 05:09 PM
Video door bell causing chime activation of coil
by gfretwell. 12/10/18 12:35 AM
Conduit fill Calculations
by gfretwell. 12/08/18 08:39 PM
Swimming Pool question
by HotLine1. 12/05/18 12:37 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 19 guests, and 13 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Receptacle Placement #100200
10/27/06 02:18 PM
10/27/06 02:18 PM
J
JoeRossi  Offline OP
Member
Joined: Jan 2003
Posts: 26
Washington, NJ
Can a receptacle be placed directly behind a kitchen or bathroom sink? I have always taken that the 24" and 36" are measured from the edge of the basin. Therefore to me the area inside the edges were restricted.

Any thoughts?
Thanks


Joe Rossi
2017 / 2014 NEC & Related Books and Study Guides
Re: Receptacle Placement #100201
10/27/06 02:35 PM
10/27/06 02:35 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,493
Michigan USA
Joe- the answer is yes to both locations. As a matter of fact the graphic in the '05 code even illustrates it for a kitchen sink. I've always had reservations about locating a receptacle on the wall behind a cooktop above the cooktop but I can't see any restrictions on that either. One could use the inspectors judgment that it would be subject to physical damage (heat) but I guess the inspector could be correct. The other part of the question might be- What would you use it for? That's right there with the restriction on puting a receptacle in a shower (Prohibited by code unless listed for that purpose) I don't even want to know what you'd use a receptacle in a shower for.


George Little
Re: Receptacle Placement #100202
10/27/06 02:46 PM
10/27/06 02:46 PM
J
JoeRossi  Offline OP
Member
Joined: Jan 2003
Posts: 26
Washington, NJ
Thaks, if you look at the illustration of Figure 210.52 it shows space behind the sink. I came across a sink with about 2" of counter top behind it and a receptacle directly behind the facut. I felt it would be more dangours if someone wanted to use it. Other than a safety factor, I do not see any code that would inhibit it.


Joe Rossi
Re: Receptacle Placement #100203
10/27/06 04:06 PM
10/27/06 04:06 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,493
Michigan USA
We do have a little bit of a safety net here with GFCI protection required for these locations.


George Little
Re: Receptacle Placement #100204
10/27/06 04:45 PM
10/27/06 04:45 PM
Y
yanici  Offline
Member
Joined: Sep 2006
Posts: 58
Atlantis
I was on another forum where a member wrote in. He was on a job for a guy who had a large rental complex. It seems that this owner wanted a receptacle on the wall directly above each electric range. He couldn't seem to get how a cord would end up in the soup. The electrician was trying to appease this guy because he gave them a lot of work. Never did hear the final outcome.

Re: Receptacle Placement #100205
10/27/06 05:03 PM
10/27/06 05:03 PM
S
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
Ughck! Amperage flavored soup!

I have never in my life seen a receptacle placed directly above an oven range on purpose.

Re: Receptacle Placement #100206
10/27/06 08:12 PM
10/27/06 08:12 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
They used to sell elecgric ranges with a NEMA 5-15 receptacle built in.


Greg Fretwell
Re: Receptacle Placement #100207
10/27/06 08:30 PM
10/27/06 08:30 PM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Code doesn't consider the sink to be countertop space, so I'd tend to think that a receptacle behind the sink, while not prohibited, might not count towards the 24/48" requirement. Kinda splitting hairs there, though.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 7,050
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,237 Are you busy
189,201 Re: Forum
178,885 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.005s) Memory: 0.9929 MB (Peak: 1.1489 MB) Zlib enabled. Server Time: 2018-12-16 10:28:48 UTC