Disco under the skirt in the '99 cycle, there would be no debate, its a violation.


1999
Quote
680-12. Disconnecting Means
A disconnecting means shall be provided and be accessible, located within sight from all pools, spas, and hot tub equipment, and shall be located at least 5 ft (1.52 m) from the inside walls of the pool, spa, or hot tub.

2002 changes the wording and organization of the article.

2002
Quote
680.12 Maintenance Disconnecting Means.
One or more means to disconnect all ungrounded conductors shall be provided for all utilization equipment other than lighting. Each means shall be accessible and within sight from its equipment.

And... (Which is something else in the '99)
Quote
680.22(C) Switching Devices. Switching devices shall be located at least 1.5 m (5 ft) horizontally from the inside walls of a pool unless separated from the pool by a solid fence, wall, or other permanent barrier. Alternatively, a switch that is listed as being acceptable for use within 1.5 m (5 ft) shall be permitted.
Panelboards, time clocks, pool light switches, and so on, where located not less than 5 ft horizontally from the inside walls of a pool without a solid fence, wall, or other permanent barrier, must be out of reach of persons who are in the pool, thereby preventing contact and possible shock hazards.

I wonder what 2005 has for wording....