I had the privilege of a tour of a State-of-the-Art Data Center / Disaster Recovery Space designed building recently. I was in awe with the electrical systems within the facility.

The building consisted of 314000sq feet on three floors...here are some specs...

ELECTRICAL: Redundant service (13.8K volt)feeds six 2500kVA substations (capacity for 15)

EMERGENCY POWER: Eight 2MW Caterpillar diesel generators located on roof (capacity for 15) with three 30,000 gallon underground tanks to provide a minumum of 72 hours of continuous operation at full load.The original thought was to have the generators in the basement of the building near the service, but the mechanical contractor estimated that the wind velocity through the floor would have to be at speeds of up to 90 mph to remove the heat produced when running at full capacity, so they were put on the roof.I think he said there were three 1800kw load banks used for exercising the generators.

UPS SYSTEMS/PDUs: Multiple liebert UPS units installed and operating, each with C&D wet cell battery strings. 100 watts psf of redundant power to Raised Access Floors. The signal reference grounding grid work under the 3rd floor RAF has .9 ohms to earth. Dual-fed static switch PDUs installed and avalable for tenant use.

HVAC: 4500 tons of cooling capacity delivered from five 900 ton York chillers and 5 Marley cooling tower cells.

FIBER PROVIDERS: 13 fiber providers avaiable at prefered pricing.

EMERGENCY WATER: A 400,000 gallon water storage tank beneath the parking lot provides continuous chiller service at full capacity in the event of municipal interuption.

STRUCTURE: Steel frame with brick and glass pre-cut screenwalls.

An interesting method of cable support was used for tieing down the cables in the cable trays run throughout the floor area. They used string wraped around the cables to tie them to the tray instead of tiewraps.This method was used every 2 feet. Must have taken days.Each tie was done the same way.

It took 18 months and 100 million to construct the facility.