I have job coming up ( the wood working plant previously posted), that I am to set a 480 volt panel on. The building at one time had some sort of 480 volt panel. The panel has been removed, and all that is there now, is about a 20" X 20" junction box with 2 pair of feeders coming into the back of the box. The feeders seem to be paralled. There are 4 3/0's in each pvc run into this junction box. It is coming from an outside transformer.
I'm now pretty sure they had a 400 amp panel originally. I have a quesion now though while looking through the code. The 3/0's are good for 200 amps, and parralleled you have 400 amps. The service is 480/277 volts. The fourth wire in each conduit, I assume is the neutral. In this application, does the neutral not have to be counted when derating? Obviously it don't. I guess this comes with the code reference, of when the neutral is only used to carry the unbalanced current from other conductors, it don't have to be counted. Am I correct in this?? Another question, in what situation would the neutral be counted as a current carrying conductor?? Thanks again... I deleted most of the original message. It was not needed now. Thanks again, Steve

edited again. Forgot to say, that I will probably go back with a 400 amp. 30 circuit panel with main breaker, then the wires will probably be long enough to reach the lugs on the new panel ( bottom lugs ). With the machinery that may be added, the extra amperage and spaces might come in handy down the road, since it seems this project is not exactly planned out like I would like it by the owner.... Still on the drawing board .. Steve [Linked Image]

[This message has been edited by sparkync (edited 03-03-2005).]

[This message has been edited by sparkync (edited 03-03-2005).]

[This message has been edited by sparkync (edited 03-03-2005).]