Romex is listed as a 60 degree assembly.
The THHN wire inside romex is listed as a 90 degree wire.
By putting romex in pipe, you are throwing away 30 degrees of de-rating, before you do anything else.
Also, the inside of conduit can sometimes be considered a wet location; romex is not allowed in wet locations.