The statment:
Quote
There are no UL Listed overcurrent devices, of any type or manufacturer, that are rated for use with wire/cable sized using the 90C ampacity column.
Needs to be qualified a little bit by saying for 600v or less. Once you get over 600v. there are terminals rated for 90 degree C and the 90 degree column in wiring tables is acceptable for termination.