Fire pump with Normal feed and Alternate source. A Stand By Generator.
Normal power Service Tapped ahead of other service run To a Disconnect SW. rated at Locked Rotor Current. Then to transfer sw. Then to mtr. Question if the Transfer Switch is a Fire Pump rated transfer Switch is the locked rotor current Disconnect Sw. required on the Normal service side or even on the load side.
Note (695.4b) Over current Device SHALL BE PERMITTED (as I read it Not required.
If as I read it Switch is NOT required Transfer Switch would be required to be located at Nearest point of entry like a service. Would like Some Imput on this please.