I disagree. The overcurrent protection of this panel is the feeder breaker at the house. The overcurrent protection is permitted to be in the panel or anywhere on the supply side of the panel. The only issue here is the number of disconnects permitted. As the others have said you can not have more that 6 breakers in this panel unless a main breaker or other disconnect is installed. The disconnect could be a non-fused switch.