Starting a renovation job at a car dealer in No. VA and looked around the electric room. Dear GOD! To start a small list:
110.12 ( a nice one that covers all crappy work), 110.22 (NO PANEL SCHEDULE AT ALL [Linked Image] AND THERE ARE THE MDP AND SIX SUB PANELS), 348.30 (A), 348.30(B), 314.28 (C), 314.23 (A), 410.12, 410.16 (C), 410.18 (A), 410.22, 410.28 (These last ones cover support, covers on boxes and luminaries, and general instillation of lighting), 250.146 (non-grounded receptacles with sensitive electronics plugged in), 250.53 (cover mount receptacle ground bonding jumper), 400.8 (uses not permitted for flexible cord), 358.26 (number of bends in an EMT run), 314.17 (openings to be closed), 110.26 (spaces about elec. equip.), 300.14, and 210.4 (D) (identification of ungrounded conductors). What a mess. The feeds to all the RTU's were done with unmarked red wire (#2, all, despite a feed for a 30A, 50A, and 90A RTU with no bond bushings despite concentric KO's), there was flex all over the ceiling, open boxes, etc.) Nasty stuff [Linked Image]

These guys are about a mile from the Pentagon! It’s a good thing it’s a different jurisdiction, or I would have serious worries about that building. Not good at all.