Norm
The 2500 volt DC test does not provide an adequate check of the insulation integrity.
Is the cable in use now? I would want to Hi Pot test the cable. New 15 kv cable is tested at about 60 kv but that is not what you want on cable this old. Check with the mfg annd see if they can give you a value to test the cable.