George:

I believe the minimum and maximum breaker size of 35 amps is for motor start up while the full load running amps of the unit is 22 amps. The oversized breaker is so the start up current does not trip the device. # 10 wire is what I would use to feed the unit, since it would not demand more than 22 amps of continuous load during operation.